Old January 24th, 2023, 08:49 AM   #196
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 6,147
Another typo at Subroutine 50 Test Pressure, Rung 5: high/low tolerance tests are reversed?
__________________
_
Brian T. Carcich
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
iii) Measurement is hard.
iv) I solemnly swear that I am up to no good
v) I probably have the highest ratio of forum posts to actual applications in the field (∞).
vi) Hakuna matata.
  Reply With Quote
Old January 24th, 2023, 09:03 AM   #197
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 6,147
Subroutine 30 Discrete Valves, Rung 2, Compare of DS1 Sequence Step to 60 (Test Pressure Hold) should be <, not ≤, because the pump should not be available to restore the test part pressure if it drops.

By the same reasoning, in Subroutine 99 Outmap, Rungs 6 and 7 should write 0.0 to the I/P transducer during step 60, the ≤ 60 on Rung 6 should be < 60, and the > 60 on Rung 7 should be ≥ 60.
__________________
_
Brian T. Carcich
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
iii) Measurement is hard.
iv) I solemnly swear that I am up to no good
v) I probably have the highest ratio of forum posts to actual applications in the field (∞).
vi) Hakuna matata.
  Reply With Quote
Old January 24th, 2023, 09:48 AM   #198
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 4,659
Regarding slowly increasing the pressure the pump will not run at probably 6-7 ma (assume 10 psi, so I suggest when you start the pump on a oneshot (perhaps an extra step you have plenty spare as it appears that all posts so far are keeping the steps of 10) for example if step 10 was to start the pump, from 0 (Idle) move 5 or what ever into the sequence step number, move say 7 ma (min pump start air pressure) then move 10 into the seq register this in itself is a oneshot so then you have a starting air pressure rather than starting at 0 & the pump will not run until the I/P (Current to pressure) (yes that is what it is called not a transducer that is ambiguous as it also refers to a signal back (analog input)rather than analog output).
See pic on extra step to pre-load (you may have to change the step number to fit in what others or you have done).
Attached Images
File Type: png Extra step.png (18.1 KB, 30 views)
  Reply With Quote
Old January 24th, 2023, 12:53 PM   #199
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 6,147
Another bug in Subroutine 20 States, I think; see the attached image.
Untitled.png
What started me thinking about this is, after the NO Contact C2 HMI_PB_Cycle_Stop on Rung 3, the NC Contact C2 HMI_PB_Cycle_Stop on Rung 4, which is not necessary:
  • If C2 is 1 on a scan, then Rung 3 will trigger, which will prevent Rung 4 from triggering even if the NC C2 is not there.
  • So the only way Rung 4 can trigger is if C2 is 0 in the first place, plus all the other contacts on Rung 4, so the NC C2 is redundant.
Also, this is the only reference to C1 HMI_PB_Cycle_Start in the entire program, so pressing the HMI start button is the only way to affect anything, and all it does is prevent the 10=>20 transition. Then there is the issue whether the HMI sets and clears the button's bits, or if those bits are set-and-forget.

So maybe that is supposed to be C1 in Rung 3?

P.S. I assume each of those bits is "active" (i.e. to start or to stop) when its value is 1.

Or maybe this is what was intended: pressing HMI Stop transitions to State 10 (Idle) from any state; pressing HMI Stopm, while both (i) in State Idle AND (ii) test part is depressured, transitions to State 20 Ready.
Untitled2.png
__________________
_
Brian T. Carcich
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
iii) Measurement is hard.
iv) I solemnly swear that I am up to no good
v) I probably have the highest ratio of forum posts to actual applications in the field (∞).
vi) Hakuna matata.
  Reply With Quote
Old January 24th, 2023, 04:39 PM   #200
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 6,147
This might work. I wonder if there is a conversion app from Click to DoMore; this should be straightforward to simulate.


[Edited: fixed a typo in the program]
Attached Files
File Type: pdf HPTv004drbitboy.pdf (1.13 MB, 0 views)
File Type: zip Hydrostatic Pressure Tester v004_drbitboy.zip (14.8 KB, 1 views)
__________________
_
Brian T. Carcich
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
iii) Measurement is hard.
iv) I solemnly swear that I am up to no good
v) I probably have the highest ratio of forum posts to actual applications in the field (∞).
vi) Hakuna matata.

Last edited by drbitboy; January 24th, 2023 at 04:52 PM.
  Reply With Quote
Old January 24th, 2023, 05:26 PM   #201
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 6,147
Here are some of the key pieces of the algorithm that sets the air pressure regulator setpoint. At its core it does summat similar to what the human operator seems to be doing:
  • initially turn "knob" most of the way to a fixed value that should bring the system nearly to the setpoint
    • With the known pump pressure ratio, the Click can do this in one go
    • This is State 20 Start Pump
    • Transition to next state at 10psi
  • Leave knob at initial fixed value, wait for pressure to settle
    • it should settle a bit below the setpoint
    • This is State 30 Pump to initial stall
    • Transition to next state when settled
      • current "settled" criterion is empirical and untested
  • Sneak up on setpoint from there
    • "Small moves, Ellie, small moves" - tweak "knob" by ~1psi
    • compare feedback from pressure sensor to setpoint
      • stop if all sampled pressures for a full second are above the setpoint
    • repeat at 1Hz
    • This is State 40 Pump until test pressure
Not shown are the 1-second group sampling metrics, used to determine "settled" and "above setpoint," a but they are simple.
__________________
_
Brian T. Carcich
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
iii) Measurement is hard.
iv) I solemnly swear that I am up to no good
v) I probably have the highest ratio of forum posts to actual applications in the field (∞).
vi) Hakuna matata.
  Reply With Quote
Old January 25th, 2023, 07:25 PM   #202
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 6,147
Update: I forgot to attach the image to that last post; here it is below.


Quote:
Originally Posted by drbitboy View Post
here are some of the key pieces of the algorithm that sets the air pressure regulator setpoint. At its core it does summat similar to what the human operator seems to be doing:
  • initially turn "knob" most of the way to a fixed value that should bring the system nearly to the setpoint
    • with the known pump pressure ratio, the click can do this in one go
    • this is state 20 start pump
    • transition to next state at 10psi
  • leave knob at initial fixed value, wait for pressure to settle
    • it should settle a bit below the setpoint
    • this is state 30 pump to initial stall
    • transition to next state when settled
      • current "settled" criterion is empirical and untested
  • sneak up on setpoint from there
    • "small moves, ellie, small moves" - tweak "knob" by ~1psi
    • compare feedback from pressure sensor to setpoint
      • stop if all sampled pressures for a full second are above the setpoint
    • repeat at 1hz
    • this is state 40 pump until test pressure
not shown are the 1-second group sampling metrics, used to determine "settled" and "above setpoint," a but they are simple.
Untitled.png
__________________
_
Brian T. Carcich
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
iii) Measurement is hard.
iv) I solemnly swear that I am up to no good
v) I probably have the highest ratio of forum posts to actual applications in the field (∞).
vi) Hakuna matata.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
plc program omron errors ngoclan LIVE PLC Questions And Answers 0 October 14th, 2014 07:03 AM
Plc suggestion aec LIVE PLC Questions And Answers 36 January 2nd, 2012 02:56 AM
Mitsubishi GX Developer - uploading/downloading program from PLC mkac LIVE PLC Questions And Answers 7 June 17th, 2010 06:31 AM
SLC 500 Ethernet Setup JSPLC LIVE PLC Questions And Answers 3 June 1st, 2010 06:15 PM
Simulator, Simulation, Shadow Code Terry Woods LIVE PLC Questions And Answers 1 January 2nd, 2005 03:40 PM


All times are GMT -4. The time now is 02:40 AM.


.