![]() ![]() ![]() ![]() This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc. |
||
![]() |
![]() |
#1 |
Lifetime Supporting Member
![]() ![]() Join Date: Apr 2019
Location: Oklahoma
Posts: 54
|
RSNetwork for DN Point IO
Hey guys
Im thinking about using some point IO on and old SLC 5/05 with a device net scanner. I have RS Networx and have looked at some other scanners that we have on other machines to see how it works. I was able to add the 1734-ADN but do not see how to add the IO modules to the IO adapter. I can add the IO modules but they show up with a different node address. Anyone have any pointers on what I am missing. |
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
|
POINT I/O with DeviceNet was a weirdly flexible product. The backplane of POINT I/O is really just DeviceNet at 1MB.
When you used a 1734-PDN, the DeviceNet network basically passed the packets straight through to the connected modules. They all took up a whole DeviceNet node number of their own, and you would see them individually on the RSNetworx project. The 1734-ADN is a different animal: it is itself a Scanner on the POINTBus side, and an Adapter on the DeviceNet side. So you actually need two different RSNetworx files: one to map the POINT modules into the -ADN's Scanner side, and another to map the -ADN's assembled I/O image into the Scanner from an PLC/SLC/Logix. You would almost expect to be able to double-click on that 1734-ADN and open up another instance of RSNetworx or an applet to configure it, wouldn't you ? But you dont: you create an all-new project file with the 1734-ADN as a Scanner. It's clunky at best, which is one reason it's been almost entirely supplanted by the 1734-AENT and EtherNet/IP. But it does work ! |
![]() |
![]() |
#3 |
Lifetime Supporting Member
![]() ![]() Join Date: Apr 2019
Location: Oklahoma
Posts: 54
|
Thanks Ken, if I had looked hard enough I would have seen that in chapter 5 of the 1734-ADN manual.
|
![]() |
![]() |
#4 |
Lifetime Supporting Member + Moderator
|
I built a system with what could be best described as "failover" I/O where a ControlLogix Redundancy system ran remote chassis on ControlNet each of which had a 1756-DNB that scanned some special sensors as well as several 1734-ADN adapters. Each ordinary discrete or analog sensor was wired to two separate POINT I/O modules.
So I needed two *.DNT files for the two 1756 Scanners, and a total of six *.DNT files for the 1734-ADN adapters, four of which were identical except for their serial numbers. Let's just say that when I came back to it after six years I was grateful for 2010-me writing good notes. |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Point IO burned up. | dftmaint | LIVE PLC Questions And Answers | 5 | May 6th, 2021 09:52 PM |
1734 ADN Point IO status | bornwild | LIVE PLC Questions And Answers | 6 | October 17th, 2018 07:41 AM |
Point IO Analog scaling | kjacoby | LIVE PLC Questions And Answers | 12 | May 24th, 2017 01:06 PM |
Point IO Cable Length | Ray S | LIVE PLC Questions And Answers | 4 | January 7th, 2013 12:18 PM |
Point IO 4 Point AC-DC Relay Output configuration | JNS | LIVE PLC Questions And Answers | 1 | April 27th, 2011 12:51 PM |