Hey guys

Im thinking about using some point IO on and old SLC 5/05 with a device net scanner.

I have RS Networx and have looked at some other scanners that we have on other machines to see how it works. I was able to add the 1734-ADN but do not see how to add the IO modules to the IO adapter. I can add the IO modules but they show up with a different node address.

Anyone have any pointers on what I am missing.
Attached Images
File Type: png Screenshot 2023-01-24 at 6.17.11 PM.png (185.9 KB, 27 views)
  Reply With Quote
Old January 24th, 2023, 07:39 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 17,254
POINT I/O with DeviceNet was a weirdly flexible product. The backplane of POINT I/O is really just DeviceNet at 1MB.

When you used a 1734-PDN, the DeviceNet network basically passed the packets straight through to the connected modules. They all took up a whole DeviceNet node number of their own, and you would see them individually on the RSNetworx project.

The 1734-ADN is a different animal: it is itself a Scanner on the POINTBus side, and an Adapter on the DeviceNet side.

So you actually need two different RSNetworx files: one to map the POINT modules into the -ADN's Scanner side, and another to map the -ADN's assembled I/O image into the Scanner from an PLC/SLC/Logix.

You would almost expect to be able to double-click on that 1734-ADN and open up another instance of RSNetworx or an applet to configure it, wouldn't you ? But you dont: you create an all-new project file with the 1734-ADN as a Scanner.

It's clunky at best, which is one reason it's been almost entirely supplanted by the 1734-AENT and EtherNet/IP.

But it does work !
  Reply With Quote
Old January 24th, 2023, 09:51 PM   #3
eight_bools
Lifetime Supporting Member
United States

eight_bools is offline
 
Join Date: Apr 2019
Location: Oklahoma
Posts: 54
Thanks Ken, if I had looked hard enough I would have seen that in chapter 5 of the 1734-ADN manual.
  Reply With Quote
Old January 24th, 2023, 11:16 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 17,254
I built a system with what could be best described as "failover" I/O where a ControlLogix Redundancy system ran remote chassis on ControlNet each of which had a 1756-DNB that scanned some special sensors as well as several 1734-ADN adapters. Each ordinary discrete or analog sensor was wired to two separate POINT I/O modules.

So I needed two *.DNT files for the two 1756 Scanners, and a total of six *.DNT files for the 1734-ADN adapters, four of which were identical except for their serial numbers.

Let's just say that when I came back to it after six years I was grateful for 2010-me writing good notes.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Point IO burned up. dftmaint LIVE PLC Questions And Answers 5 May 6th, 2021 09:52 PM
1734 ADN Point IO status bornwild LIVE PLC Questions And Answers 6 October 17th, 2018 07:41 AM