PLC going into program mode by itself

Hello friends

I think this is the second post about this all over the internet, first one was in 2013 by some guy from Canada who experienced the same as me.

I have a CLX processor that turned into program mode by its own, nobody turned the keyswitch (the key was not inserted), the keyswitch was in REM mode and the PLC was running ok.

PLC is ControlLogix 1756-L75

I turned it into remote run by studio5000.

I found nothing in the major or minor faults, all I/O is working ok.

It was 2 weeks ago, until now nothing is changed, just turned it into remote run and continue working normally.

Please, do you know what else could cause a CLX goes into rem program mode by its own? where should i check? do i have to call an agent of the paranormal and occultism to find an answer?



I haven't been able to sleep since then

Last edited by Kefren; January 23rd, 2023 at 12:25 PM.
  Reply With Quote
Old January 23rd, 2023, 01:02 PM   #2
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Nashville, Tennessee area
Posts: 3,440
If there was no key and the processor went into remote program mode, no faults, i would say that one of 2 things may have occurred.
1. someone got on the plc with a laptop and turned the plc into remote program mode.
2. someone has a key to the plc (they are all the same) and turned it to program mode and then remote run mode.
others may have a better idea, but this is the only two things i can come up with.
regards,
james
  Reply With Quote
Old January 23rd, 2023, 02:11 PM   #3
Aardwizz
Member
United Kingdom

Aardwizz is offline
 
Aardwizz's Avatar
 
Join Date: Dec 2017
Location: Swindon
Posts: 333
Grasping at straws

There might be one other way:

PLC experiences an unrecoverable fault.
PLC has a fault routine to clear faults / fault codes.
But since the fault is unrecoverable, the PLC cannot go back into RUN mode, yet is no longer "faulted". Therefore it must be in PROGRAM mode.
  Reply With Quote
Old January 23rd, 2023, 04:02 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,856
There is nothing paranormal or inexplicable about it.

The most likely explanation is that someone using RSLogix 5000 switched the controller into Remote Program module. Maybe they were diagnosing something and did it accidentally then hushed it up: that happens all the time.

It's equally possible that the controller faulted and was restored to Remote Program after a power cycle, or a keyswitch cycle, because that's what it is configured to do.

If this were my system I would check the webpage of the Ethernet module and see the Uptime value for that module. That could tell you if there was a power cycle you don't know about.

When stuff happens on night shift, the probability of human error hidden by human embarrassment is very, very high.
  Reply With Quote
Old January 23rd, 2023, 09:15 PM   #5
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,221
I work in a couple of factories that it is their rule all key switches are kept in RUN unless program updates are required. No REM allowed, I have to remember to turn the key back after being online with it..
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
  Reply With Quote
Old January 25th, 2023, 11:04 AM   #6
Kefren
Member
Nicaragua

Kefren is offline
 
Join Date: Jul 2017
Location: León
Posts: 11
The only person with access to plc software is a college and me, at the time this happend we were both in the same room, the network is fully isolated to internet connection and we use a laptop for programing, the software is not installed in the operation stations

The keyswitch was in REM and the key was not inserted, also the cabinet was locked

The PLC that i am talking about is a set of two primary with synchronize

I also checked for the major and minor faults and found nothing

I hope this post help to resume tips to check to understand what happened
  Reply With Quote
Old January 25th, 2023, 01:18 PM   #7
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,570
Quote:
It's equally possible that the controller faulted and was restored to Remote Program after a power cycle, or a keyswitch cycle, because that's what it is configured to do.
Something Ken said.. Power surges can cause this. Also surge protection on all inductive loads.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old January 25th, 2023, 02:10 PM   #8
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,856
So it's a ControlLogix Redundancy system ?

You need to double-check your assumptions about the security and isolation of your system. I believe that you believe that your system is isolated, well-administered, and physically secure.

But I've seen people who have to work on isolated, well-administered, and physically secure systems devise clever and well-hidden workarounds, and hiding them from the bosses is part of that process.

If it's a ControlLogix Redundancy system, then the 1756-RM2 module logs may also provide some information about the transition to PROG mode.
  Reply With Quote
Old January 25th, 2023, 02:49 PM   #9
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,221
Quote:
Originally Posted by Mickey View Post
Something Ken said.. Power surges can cause this. Also surge protection on all inductive loads.

This makes it a good idea to keep ControlLogix keys in RUN at all times unless need to do online edits, but on a redundancy system editing the CPU and the RM2 would have to be done at the same time, wouldn't they?



I've ever attempted an online edit of a redundancy system as I'm thinking it's going to be similar to the GuardLogix in editing (not possible)



Can someone tell me if I'm right or guessing wrong about this?
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
  Reply With Quote
Old January 25th, 2023, 03:29 PM   #10
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,856
Actual ControlLogix Redundancy, with properly set up RM/RM2 modules and pairs of CPUs and network modules, looks like just one CPU to the user.

The paired controllers have to be in the same keyswitch mode, and it's normal to leave them in REM mode so that you can perform online edits.

ControlLogix Redundancy historically has more subtle bugs than ordinary ControlLogix because it's so much more complex. But in general, a failure or bug causes a fault or record. The system doesn't just "flip to REM PROG", even though ending up in REM PROG is a common result of major unrecoverable faults and power cycles.

Every instance I've personally investigated where an isolated, secured, well-administered system had an unexplained malfunction that was consistent with an unauthorized user or a fault and power cycle... actually had an unauthorized user or a fault and power cycle.

Last edited by Ken Roach; January 25th, 2023 at 03:38 PM.
  Reply With Quote
Old January 25th, 2023, 03:40 PM   #11
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,221
Quote:
Originally Posted by Ken Roach View Post
Every instance I've personally investigated where an isolated, secured, well-administered system had an unexplained malfunction that was consistent with an unauthorized user... actually had an unauthorized user.

I worked in a shop that had Bubba working 3rd shift that had an HMI in his locker he would program to change a single bit or value to override the limits set in the HMI's.
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
  Reply With Quote
Old January 25th, 2023, 07:13 PM   #12
lostcontrol
Lifetime Supporting Member
New Zealand

lostcontrol is offline
 
lostcontrol's Avatar
 
Join Date: May 2009
Location: NeverSayNever
Posts: 942
Quote:
Originally Posted by I_Automation View Post
I worked in a shop that had Bubba working 3rd shift that had an HMI in his locker he would program to change a single bit or value to override the limits set in the HMI's.
This is classic 🌭
  Reply With Quote
Old January 25th, 2023, 07:36 PM   #13
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,221
Quote:
Originally Posted by lostcontrol View Post
This is classic ��

This is why I program the limits in the PLC and reject any value out of my limits, and the limits are not tags that can be changed but values that would need an online edit to change.

I also have a SetPoint tag that is used and an HMI_Entry tag. Changing the SetPoint directly the PLC will change it back to the HMI_Entry value the next scan, Changing the HMI_Entry to an out of range value is ignored and that tag is reset to the SetPoint. The only way around would be write to SetPoint AND HMI_Entry on the same scan - which an HMI that can do that I haven't seen yet (but not saying one doesn't exist)



As far as changing bits I try to have checks so they don't get changed unless conditions are right, but toggling a bit by an errant HMI is hard to overcome.


Here's a shot from my home automation SLC of how I change setpoints
Attached Images
File Type: png Capture05.PNG (21.6 KB, 124 views)
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors

Last edited by I_Automation; January 25th, 2023 at 07:50 PM.
  Reply With Quote
Old January 26th, 2023, 03:50 AM   #14
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 2,259
Quote:
Originally Posted by I_Automation View Post
Here's a shot from my home automation SLC of how I change setpoints
Silly question, but is this living permanently in your home controller? I just find it hilarious someone programming a PLC to do something on Christmas morning. Is it pre-heating the oven? :P
  Reply With Quote
Old January 26th, 2023, 05:44 AM   #15
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,221
Quote:
Originally Posted by cardosocea View Post
Silly question, but is this living permanently in your home controller? I just find it hilarious someone programming a PLC to do something on Christmas morning. Is it pre-heating the oven? :P
My home automation system (1 SLC5/05, 3 5/03's, 1 5/04, 1 ML1400, 2 Siemens S7-200's) controls about 140 circuits of Christmas lights and 40 circuits of Halloween lights along with 7 security lights, gate locks, fire and flood alarms, solar battery charging, 6 outdoor outlets controlled, 6 temperatures monitoring, electric blanket control, power changeover for air conditioner compressor when the controlled meter is turned off, slow cooker control, and more. Plus a fully functioning traffic light with left turn lights, Walk/Don't, Prepare To Stop When Flashing, School Speed When Flashing, antenna tower lights, block control and street lamps for a model train set I haven't built yet.
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Problem with upload/download of program with OMRON CJ1M PLC AB2005 LIVE PLC Questions And Answers 6 August 27th, 2016 08:23 AM
PLC loose program after power outage or if PLC gets turned off koliza1 LIVE PLC Questions And Answers 5 August 3rd, 2016 05:08 PM
How to determine if PC file matches PLC program (SLC5/05) ryangriggs LIVE PLC Questions And Answers 7 July 12th, 2016 01:23 PM
Mitsubishi problem gunther LIVE PLC Questions And Answers 11 June 17th, 2006 11:01 AM
Let me know how to communicate between two plc & how to configure .... farooq mohd LIVE PLC Questions And Answers 3 February 13th, 2006 11:53 PM


All times are GMT -4. The time now is 02:41 AM.


.