Port conflict after autoconfigure in RSLinx
Good day all. I am trying to connect via RS-232 port to a SLC-5/03. I get it to autoconfig in RSlinx while creating the driver however, it then pops up an alert that reads, "RSLinx Classic has failed to configure the com port!". I select Ok, status shows running however, it says "Port Conflict" to the right of the driver name. I am using a Keyspan USA-19HS (same one I have used for many years now), using Windows 11. Since I have no other serial device connected to it, what would the port conflict be? I have serial connected many times over the years and have never seen this come up. I no longer have a tech agreement with AB.
|
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
Huh, here's something else: In device mgr I changed it to com port 2 and my keyspan shows port 2. I changed it to COM2 in Linx and it wouldn't configure. I put it back to COM1 in Linx and it says Auto Configuration Successfull......and no port conflict! I know I am getting old and senile however, this makes zero sense to me.
|
![]() |
![]() |
#3 |
Lifetime Supporting Member
|
It might be something related to Windows 11, but if they still haven't buried Device Manager under too many layers of fluffy pastel b******t, try changing the COM number assigned to the Keyspan and then switch it in RSLinx.
Rant on: I hate windows 11. A customer accidentally updated an Ignition Client to it and it runs fine, except those bastages at Microsoft painted a bunch of new fluffy b*****it* layers over the top of stuff I really need to get to and it p***es me the hell off. Where the hell is my Ethernet Devices list now? They also broke Classic Shell, but Open shell came to the rescue. I was able to put my Windows 7 Classic start menu back in the lower left corner and I just ignore that fluffy bu****it menu those bastages pasted in the middle of the taskbar. |
![]() |
![]() |
#4 |
Lifetime Supporting Member
|
Yup, I did all that. My second comment was that I changed it in Device Manager, re-loaded Device Manager, saw the change had been made, went to Linx and changed it and it wouldn't configure. I changed it back to port 1 in Linx and the darned thing configured AND got rid of the port conflict however, in RSWho it doesn't show any info about what is connected to that port. This is the goofiest thing I have seen in a while!
|
![]() |
![]() |
#5 | |
Lifetime Supporting Member
|
Quote:
|
|
![]() |
![]() |
#6 |
Lifetime Supporting Member
|
|
![]() |
![]() |
#7 |
Lifetime Supporting Member
|
I believe it was hardware related. I grabbed an old 5/04 that I had laying on a shelf and it connected right away.
|
![]() |
![]() |
#8 |
Lifetime Supporting Member
|
"Port Conflict" In RSLinx definitely means that the driver couldn't run because of a COM number or similar problem with Windoze.
|
![]() |
![]() |
#9 |
Member
|
I have found that when I change a COM port number in DeviceManager I have to close RSLinx and reopen it for it to see the port.
I also have had times where RSLinx on Windows10 wouldn't see the port when it had the correct number until I stopped it and restarted it.
__________________
ivanovaautomation.com Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
rslinx connectable with printer port? | sunnycheevah | LIVE PLC Questions And Answers | 5 | June 9th, 2020 08:53 PM |
Upgrade PV600 (RS-232-DH485) comm. to ML1500 to PV+ | nicer | LIVE PLC Questions And Answers | 35 | July 1st, 2015 07:05 AM |
Allen Bradley SLC 500 fault | Frank McDonk | LIVE PLC Questions And Answers | 27 | June 6th, 2011 09:58 AM |
RSlinx 2.53 with Vista support available | Contr_Conn | LIVE PLC Questions And Answers | 7 | September 4th, 2008 09:56 AM |
RSLinx problem registering definitions from PIUNSOL.INI | Koos | LIVE PLC Questions And Answers | 0 | January 14th, 2008 12:23 AM |