Micrologix 1500 fault 21h
boyd_man
Oct 2002
South Carolina
39
I have a Micrologix (1500 LRP Series C ) controller with three Input cards and two out put cards in the expansion slots ( 1. 1769-IQ16, 2. 1769-IQ16, 3. 1769-OA16, 4. 1769-OA16, 5. 1769-OA16). I downloaded my program but when I try to go to run mode the processor faults out. ( S:1/13 = 1 and S:6 = 21h) I have looked in the fault description but can not find a fault 21. Thanks for the help you all have been giving me you have helped a lot
A really quick WAG, does the cards in the program match what is actually there? If not you might try and do a read I/O in RSLogix500 and see if this makes a diff.
I had a (1769-PA2) power supply between the I/O cards and the processor when I removed the power supply the fault went away. Does the extra power supply have to be at the end of the rack?
What is your exact set-up?
With the cards you listed I wouldn't think you need an expansion power supply. Your cards would just plug in to the base unit with a terminating end cap.
It was setup (processor, 1769-PA2, 1769-IQ16, 1769-IQ16, 1769-OW16, 1769-OW16,1769-IQ16, END CAP). I have since removed the (PA2) power supply that was added to power the Panel View.
Hi all, I am having an issue with a Micrologix 1500 1769-ECR. The PLC will not run and I’m unable to connect to diagnose the fault. When I power...
2,455
We have a ML 1500 and it faults from time to time. The floor guys always clear it before I can get to it. Is there any way to see what caused the...
1,696
We have on site 7 equal Micrologix PLC, controlling 7 equal HVAC system for 7 room. The room have redundant HVAC units. All of them have 2...
2,480
Hi, I am new. I have connected to a micrologix 1500 LRP series c. I can go on line, upload, download, but when I switch to run, it immediately...
1,701
I have a client with a Micrologix 1500 LRP processor that faulted. I had him send it to me so I could clear the fault. I plugged the processor...
15,793