I have some m340 plcs in one network and one TSX quantum, that reads data from them via io scanning, there is a pc in the same network that have ofsopc running on it, and there is another operator's pc with citect scada 7.2 client on it. OFS reads data from quantum, and this pc is described as i/o server for scada client, so everything is clear. But now I need to add a new tag from one of M340's to scada client, via ethernet and modnet protocol (not via opc), so I need to add a new i/o server for the tag and describe its network address. I don't understand what pc would be io server for modnet and how to describe it in i/o server window (network address etc). I just need to read one var with operator's scada client directly from one of m340 plc. Any help is very much appreciated!:confused:
 
Register offset

I don't know anything about Ciect but I do know that there is a 1-register difference in the communications between the M340 and the Quantum. If you don't get the expected value right away with the M340 try a holding register address that is one greater or one less than what you thought it should be.

Another difference is register alignment on float and double integer variables. The ARM CPU in the M340 is fussier than the CPU in the Quantum. This is a small price to pay for a huge cost difference in processors. Alignment won't be a problem in your system if you have an existing M340 program since the compiler already forced you to follow the rules. You may run into it if you change out the Quantum someday to a M340 or M580.

Modbus requires some tinkering - but it's like a car that is that old. It takes some patience on the part of a mechanic to make it go.
 
Allright guys, I have figured it out. There is no issues with modbus registers, as i blamed them first though))
I can actually configure any pc as an i/o server, you can not connect to m340 directly from pc described as "client", there should be an i/o server between them, or you can define your client pc as i/o server + client machine and use its IP as server's IP. Maybe it would be useful for someone. Anyway, thank you for your input.
 

Similar Topics

Hello, I need Citect SCADA communication project where we can connect Modicon Micro PLC thru TSXUSB485 cable or Delat PLC thru serial Modbus. I...
Replies
2
Views
7,332
Has anyone ever seen where you have a tag reading from the plc in scada. In this instance it's just a PEC, I set it up on one scada terminal and...
Replies
0
Views
84
Hi guys, I have experience with PLC to Excel etc...just starting on using intouch scada screens. I have an Excel sheet that uses mainly...
Replies
1
Views
127
Hello guys, I would need some help. I have installed the aveva plant scada and want to run a project. From the configurator, all are fine, as I...
Replies
0
Views
95
Is it possible to connect a PC with running WinCC Advanced or Unified to a siemens PLC such as S7-1200 across different subnets? The computers can...
Replies
0
Views
74
Back
Top Bottom