ScadaPack 350 and Sensaphone 2000

acrd

Member
Join Date
Jan 2014
Location
Port Alberni
Posts
2
Looking at updating a small (1000 customer) water distribution system
The main site has a ScadaPack 357 and there are 4 remote locations using ScadaPack 334's.
They are running GE Proficy iFix on a PC at the main site.
The main site also has a Sensaphone 2000 for alert notification via phone, pager and email.
The problem is that due to the fact that the sensaphone reads data from the plc directly, the threshold settings for alarms must be set separately in the iFix software and sensaphone.
I don't quite understand how to resolve this as I don't think you want whatever device you use to send alert notifications to read the thresholds from the pc as you don't want that functionality dependent on the PC functioning and I don't believe there is the option to set the threshholds in the pls's themselves. May be wrong on that however.
Pretty new to this stuff and learning on the fly.
Any input would be appreciated.

George
 
Make the alarm thresholds variables that are set on the SCADA and passed down to the plc, so even without the pc running at least you will have the last values to operate as the thresholds
 
Thanks Geoff, that makes sense but I still require something to replace the sensaphone as it doesn't have enough inputs.
Also sensaphone has hard wired inputs, is there something you are aware of to replace it that is IP based so that it can read the variables from the plc for thresholds and read input addresses for levels etc. and react accordingly?
Or am I barking up the wrong tree and the ScadaPack should be replaced?

Thanks

George
 

Similar Topics

I've got 16-bit data at address 40200 on a Schneider Scapack 350. I can grab the data over Modbus TCP using Kepware at IP 172.16.1.100. When I...
Replies
8
Views
2,478
I am programming a SCADAPack 350 with Telepace Studio. I want to know if the logic in running the first scan and if the program is running...
Replies
0
Views
1,244
Hi! I've got a customer that has several SCADApacks at remote sites and I need to make changes in their cellular network system. I have the .pia...
Replies
3
Views
1,868
Hi guys, I'm working on a well pump that is supposed to use a PID loop to maintain system pressure through changing pump speed. I'm using a...
Replies
1
Views
2,218
ok fella's i have a question. i am trying to get data from a scadapack 350 in the field and use it on my wonderware. i can get data from it but it...
Replies
2
Views
1,777
Back
Top Bottom