Hi guys
I was wondering if it is possible to split a pt100 probe signal , I have a pt100 going to a controller but I would like to piggy back off the probe and put into a plc , is this posible thanks
 
See if the controller has retransmit or use signal conditioner to send to the two devices. You can potentially run 4-20ma loop through both plc and controller.
 
RTD splitter, RTD in, two analog outputs.
spec sheet
http://api-usa.com/pdf/api/apd1393.pdf

APD_1393_RTD_splitter.jpg
 
yep a double sensor, available in one housing.
you can also use a converter to 4/20 mA as this signal, can go serial from controller to data logger.
 
oh
hello
Advice : you should use crush
and requests fabricate You should ask yourself
I want to you should use
crush
and requests
fabricate
You should ask yourself
I want to signal out 4-20ma or 0-10v
 

Similar Topics

All, I have an older machine which uses Bosch Rexroth proportional control for pump tilt and relief. The pump would not tilt. We tested command...
Replies
0
Views
1,088
Hi guys I have had a thought that I could email data from a plc , but I have never done this and need your help ? I have a micrologix 1400 and a...
Replies
2
Views
1,464
Hi guys I hope you all had a great Christmas, I have a 2711p-RDT12c pvp 1250 which I would like to have a engineering page with Hmi info with...
Replies
0
Views
1,596
Hi guys I need some advice , I have a mixer using rs500 and a hmi and a silo delivery system with rs500 with a pvp ? The plc are connected via...
Replies
4
Views
1,998
Hi guys The other day I saw a youtube video on factorytalk viewpoint mobile and I thought this would help our engineers on dianostic on the...
Replies
2
Views
2,749
Back
Top Bottom