Hi All,
Can anyone give a clue as to the software and cable required to upload the program? I have no experience with this brand.

The customer just want's me to upload the program for backup.


Thanks!!
 
Last edited:
Back when the product was sold by TI the programming software for that model was a DOS-based program called TISoft. When Siemens bought TI's PLC product line, they continued TISoft for a while. I can't remember whether or not they renamed the software.
According to an old Automation Direct catalog their DirectSoft5 software was compatible with the 335-37 CPU. I don't know whether they retained that backward compatibility in DirectSoft6. As JRW suggests, your best bet for the most reliable information will be Automation Direct. They are a Koyo entity and Koyo was the manufacturer of that product in all of its iterations.
 
Initially that product required a data communications unit that plugged into the port on the CPU and converted it to SS232 or RS422. I believe Siemens offered a model with the RS232 or RS422 port built-in so you didn't need the data communications unit.
So, depending on your model, you might need the data communications unit, an RS232/RS422 converter and a 9-pin to 25-pin serial RS 232 cable to connect to the PC running the software and a USB to serial converter.
Presumably you need to extract the program from the unit so you can convert it to something more current, so it might make more sense to try to locate someone local who still has the necessary software, converters and cables to come in and extract the program for you.
 
Thanks for the Great info!!!

This facility also has nine other Automation Direct PLC's and a couple GE series one I also need to upload, so this works great!

Thanks!!!
 
False alarm on the Series 3. I just found out it was replaced with an A-D PLC, but wasn't checked off the antiquated list.

Thank You for all your help!!!
 

Similar Topics

Hi all, Got a call from a client that has several small water systems, asked me to take a look at one I've never programmed, just troubleshot a...
Replies
22
Views
5,902
Posted previously but had the wrong info, hoping to get new advice. Being a mechanical engineer, I'm not very experienced with PLCs, and what...
Replies
7
Views
2,429
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
Replies
1
Views
69
Hi, I received this SIMATIC S7-300 training kit for maintenance. When I power it up, the PLC doesn't go to RUN mode and the STOP mode led is...
Replies
7
Views
261
I'm trying to build my Classic Step 7 programming skills this weekend. I get stuck on little things that are not covered in YouTube tutorials. I'm...
Replies
7
Views
248
Back
Top Bottom