I have an application where I need to know the peak pressure of a machine and time at peak pressure. I am wondering does anyone know of an accurate way to find the time a value is at its peak in logix 5000?
 
Hi. I know I used a system time stamp routine that one of the folks here on the forum sent me. It uses a string to show date and time and one can move it into the HMI or wherever you want in logic. I used it for an indicator when a process ran it's cycle and also when the cycle counts were reset.
Just taking a WAG, one could use a compare instruction to go true when the pressure equals or exceeds what you need it to be, which would then trigger a time stamp. Just a thought really early in the morning and I hope I've helped you.
 
Last edited:
@Outlaw10801
I would use a periodic task, with high priority. Task period depends on how fast you want to capture new values, every time a higher value is capture then you write that value to a fifo together with date and time.
Do not know how your fifo size would be.
 
you can use GSV instruction with Wallclock attribute to get the time from the plc and move the value when your high pressure is triggered
 
Using a ms timer
Move time and pressure to "store" registers when timer times out.
Next rung compare if current pressure is greater than stored pressure.
If it is then move time and pressure to stored registers and continue comparisons.
 

Similar Topics

Hello all- I have a unique challenge using a customers Direct logic 06 PLC. This customer has a DC motor operating at 10 RPM which is turning a...
Replies
1
Views
131
Hi everyone, I'm working on a project that involves using a Keyence LR-X100 sensor in Studio 5000 V35 ladder logic to determine the object's...
Replies
4
Views
672
I have an analog flow signal that fluctuates with many peaks and valleys. Occasionally due to valve changes a peak value (or several) will be way...
Replies
2
Views
1,236
I've been doing Modbus for 20 odd years but almost never do I have to use a slave simulator. Until today. I used Peak HMI's freeware RTU slave...
Replies
2
Views
1,940
Hello Everyone: I have a machine in the field with a twin diaphragm pump driven by a VFD. It Produces a "sinusoidal sort of" process pressure...
Replies
6
Views
2,011
Back
Top Bottom