P2000 TC Module Setup - Burnout Detection

Using a Thermocouple module from Automation Direct on a Productivity 2000 PLC. I have a choice of "Low Side Burnout Detection" or "High Side Burnout Detection".
What is that? Is it something related to differential analog inputs, and they aren't using it for T/C's?

I did a search for "Burnout" in the PDF manuals, but they don't elaborate.
Datasheet says I have an option of "Burn-out Detection: High Side/Disable", but I'm not seeing that in software.

Last edited by keithkyll; January 12th, 2018 at 01:03 PM. Reason: More Info
  Reply With Quote
Old January 12th, 2018, 01:21 PM   #2
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is online now
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,484
Strange wording, but could it be about the behavior in response to an open circuit? If you are using the thermocouple as the feedback in a heating application, you typically want an open circuit treated as the maximum temperature for the thermocouple type so as to drive the controlled variable to zero. But there may be situations where you want an open circuit to be reported as the minimum temperature.
  Reply With Quote
Old January 12th, 2018, 06:30 PM   #3
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,772
It's what Steve explains - if the input detects an open circuit, the implication is that the thermocouple has burned out so it is not capable of providing a valid temperature signal.

Almost all heating applications use "high side/disable" for burnout which drives the indicated Process Variable (the indicated temperature value) upscale to its maximum value, which either an on-off or a PID control loop will interpret as "Too hot" (PV greater than setpoint), which will drive the output to 0%, so that the process will be driven to a safe condition, given that the sensor signal is not useable.
  Reply With Quote
Old January 13th, 2018, 08:40 AM   #4
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Heath, TX
Posts: 1,968
I expect a setting of "Upscale" for heating application, "Downscale" for cooling.
You're saying I can translate "High Side" to "Upscale"? Strange wording as Steve said?
  Reply With Quote
Old January 13th, 2018, 09:15 AM   #5
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is online now
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,484
I expect "High side" means the module will report maximum value in the event of an open circuit, but it would be one of the first things I would verify once I had the actual hardware in hand.
  Reply With Quote
Old January 13th, 2018, 09:31 AM   #6
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,394
Quote:
Originally Posted by keithkyll View Post
I expect a setting of "Upscale" for heating application, "Downscale" for cooling.
You're saying I can translate "High Side" to "Upscale"? Strange wording as Steve said?
Possibly just a poor job of Chinese to English translation.
__________________
  Reply With Quote
Old March 21st, 2018, 04:27 PM   #7
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Heath, TX
Posts: 1,968
Update - Found Answer

Found it in the software package's Help for Analog modules. Was looking for info on setting up alarms for open sensor on the 4-20mA input module. Title of help page is "I/O Module Configuration".

Temperature Modules


For all P Series temperature analog modules (NTC, RTD,and THM) there is a user selectable Burnout Detection setting that can be set to either Low Side Burnout Detection or High Side Burnout Detection. This setting determines the value that will be loaded into the channel's tag name when a sensor for that specific channel detects a failure or becomes disconnected.

Values that get loaded depend on what setting is selected:
  • Low Side Burnout = 0
  • High Side Burnout = 65535
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB 1746-HS module - IMC 110 motion controller raj LIVE PLC Questions And Answers 12 February 20th, 2009 12:36 AM
plc5 with AB 1771-DB basic module, its urgent plz help me nileshsurya LIVE PLC Questions And Answers 6 July 20th, 2005 01:45 AM
Philosophy of Equipment Error Recovery, Alarm recovery, and Re-initialization Hester LIVE PLC Questions And Answers 8 May 11th, 2004 07:40 PM
Module Fault detection in Siemens smb LIVE PLC Questions And Answers 2 August 15th, 2003 03:33 PM
SLC 5/03 data loss andydaoust LIVE PLC Questions And Answers 1 October 10th, 2002 06:38 PM


All times are GMT -5. The time now is 07:38 AM.


.