AB Logix 5573 Connection Issue

Hi All,
I ran into a machine yesterday with a 1756-L73/B (LOGIX5573) processor. I could not upload the program as the upload failed on a certain module upload. Can't remember exactly which unfortunately. Anyway, I tried to create a new program with this processor just to do some experimenting and discovered this particular processor does not exist in my drop down list. The firmware version of the processor in question is 20.13. I have Logix5000 version 20. Can someone explain how I go about this? Do I have an inadequate FactoryTalk Activation for this processor perhaps?
  Reply With Quote
Old January 12th, 2018, 03:20 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,909
Do any of the 1756 series controllers appear in your drop-down list ?

There is a "Compact Edition" of RSLogix 5000 that only supports the CompactLogix controllers and not the 1756-series ControlLogix.

I just checked my RSLogix 5000 Version 20.00.00 installation, which uses a Toolkit activation that includes every controller, and it definitely lists the 1756-L73.
  Reply With Quote
Old January 12th, 2018, 03:25 PM   #3
Maximuse
Member
Canada

Maximuse is offline
 
Join Date: Apr 2013
Location: Ontario
Posts: 16
Thanks for the reply Ken. I have all kinds of 1756 controllers listed, including the 1756-L73. What I'm missing is the L73/B. I think this might be an important distinction because the description for the L73 is "ControlLogix 5570 Controller" whereas when I try to go online or upload the dialog box states "1756-L73/B LOGIX5573". Makes me think there is definitely some sort of difference.
  Reply With Quote
Old January 12th, 2018, 03:39 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,909
The Series letter is unlikely to be the problem; it's nearly impossible to tell a Series A from a Series B controller from a firmware perspective.

I think the issue is the Module definition; I've experienced a similar problem a couple of times where I could not upload from a controller. It's been a few years and I don't recall the details (or even if they involved a v20 controller).

Try the upload again, and capture the details of the error message that appears.
  Reply With Quote
Old January 22nd, 2018, 01:50 PM   #5
Maximuse
Member
Canada

Maximuse is offline
 
Join Date: Apr 2013
Location: Ontario
Posts: 16
Forgive me for re-opening this thread but the machine is located far from where I normally travel so it took me a while to get back there. Anyways please see attached screen shots showing error message.
Attached Images
File Type: jpg Failure1.jpg (35.4 KB, 10 views)
File Type: jpg Failure2.jpg (32.1 KB, 9 views)
File Type: jpg Before_Upload.jpg (40.3 KB, 8 views)
  Reply With Quote
Old January 22nd, 2018, 02:16 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,909
Thanks very much for posting those details !

Your symptoms appear to correlate to a document in the Rockwell Automation Knowledgebase, Article ID # 565685 (Access Level: Everyone).

The error messages about the PLC/SLC mapping table are a red herring; the issue is actually a mismatch between the ControlLogix firmware and the RSLogix 5000 software that occurred when Rockwell migrated (somewhat clumsily) to a more robust digital signature method for security reasons.

The solution is to install version 20.04 of RSLogix 5000 on your computer, which will allow you to work with any version of 20.x firmware in the controller.
  Reply With Quote
Old January 22nd, 2018, 02:24 PM   #7
Maximuse
Member
Canada

Maximuse is offline
 
Join Date: Apr 2013
Location: Ontario
Posts: 16
Thanks Ken!!!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Compact logix ethernet connection problem limsgp LIVE PLC Questions And Answers 5 October 15th, 2012 07:56 PM
AB Compact LOGIX 1768-L43 to Balluff IO-Link reidyj LIVE PLC Questions And Answers 2 August 24th, 2012 02:07 AM
AB Control logix Jezz LIVE PLC Questions And Answers 1 June 21st, 2010 11:50 AM
Connection Problem between AB control logix and Citect Scada. james84 LIVE PLC Questions And Answers 7 May 24th, 2010 06:30 PM
Compact Logix Ethernet Connection dhuber LIVE PLC Questions And Answers 9 May 7th, 2010 03:39 PM


All times are GMT -5. The time now is 07:37 AM.


.