Dear Expert
I have One 231-OHF22-0XA0 8 channel analog input module.
I want to use its all 8 channel as 4-20mA.
Does it possible?. How?.

Another question is that I have 216-2BD23-0XB0 224xp CPU.
It has 2 analog input channel. Does this support 4-20mA or not.
Can i Know the wiring of it?.
Thank you
 
According to Ohms Law, it takes 200,000 volts to push 20mA through 10M ohms.

Given that incredibly high loop voltage, I'm not sure how useful channels 7 and 8 will be for ordinary 4-20mA current signals powered with 24Vdc:

current_input_on_chs_7_8_only_10_M_input_resistance-hi.jpg
 
As has been mentioned you can't use all inputs directly as mA, only 7&8 by setting S1 and S2, those inputs then have a 250ohm resistance. Do some research on ohm's law and you will find that if you pass 20mA through a 500ohm resistor you will measure 10V across that resistor, so you can easily use voltage inputs to measure current. The S7-224XP does have two analog inputs but again they are limited to Voltage.
 
The screen shot is from the link to the Siemens site (for the aforementioned AI card). It's clearly a typo/misprint because mA current dropping resistors are not in the Megohm range, evenif that's what the spec says.
 

Similar Topics

So, we have one servovalve that is very critical to machine operation and idea is (or was) to detect if valve gets disconnected from analog output...
Replies
11
Views
2,867
Hello, We monitor the temperature of a pipe via a 4-20mA temperature transducer. This goes into DB135(Read Analog Inputs). The issue I have is the...
Replies
0
Views
623
I am setting up a new system and have an s7 1214 plc with an sm1231 4x AI (6ES71231-4HD32-0XB0). It is configured for 0-10v and has no faults in...
Replies
5
Views
1,130
Hey guys! I have come across an unique issue. Hoping that I can find some solution here. I want to replace an existing S7-1214 DC/DC/DC plc with...
Replies
15
Views
4,641
When using Turck BL20 analog and Siemens S7 can someone tell me if the scaling in S7 is still 0-27648 (for 0-10vdc/4-20ma) or is it something...
Replies
3
Views
1,836
Back
Top Bottom