Hi all,
iam facing problem in allenbradely analogue input module 1756-IF8, i.e one of the channel continuously fluctuating (CH NO-4). Iam not able to find out root cause. Kindly help me in this matter. I have checked field side and module replaced but problem not yet solved.
 
1. "Continuous flucutations" is a common description for what people use when a PID loop is not turned properly and the process cycles. Fluctuations due to incorrect PID tuning are not solved by blaming the analog input.

Is continuous fluctuations "noise"? What are the characteristics of the fluctuations? Using numbers, describe what is happening.

2. Check the output of the field device to see if it is behaving exactly as expected with a separate calibrator/DVM/ whatever (check it at the PLC using the wiring to the PLC).

Substitution of a field device does not neccessarily catch a problem that is affecting the operation a field device that is merely a reflection of a systematic problem outside of the device, for instance, a DP transmitter's impulse tubing is leaking or is blocked. A working, functional replacement will indicate the same problem as the functional device being replaced.

3. Check the AI channel with a simulated input (4-20mA?) to see if it is stable.
 
yes also check the earthing, the screen of the cable must be properly connected in one side only to instrument earth, otherwise you will create current loops.
 
Also check that noise isn't being introduced on that channel's cable run by being in close proximity to cables carrying large currents, VFD motor cables, etc.
 
If the instruments connected to this analog input are loop powered, then this fluctuation of analog input signal may have to do with loop resistance. i.e @ close to 100% process measurement current loop will be close to 20 mA and the loop resistance will drop the voltage across the transmitter to below what it requires causing it to shut down (if it is of smart type) the current of the loop then decreases increasing the voltage across the transmitter which will cause it to boot-up, then the transmitter trying to match the process measurement of nearly 100% will try to inject close to 20 mA again in the loop and the voltage drop will occur again resulting in it shut-down. and it goes again and again which causes your fluctuation.
Hope you understand me, you may want to check it out.
 

Similar Topics

Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
0
Views
27
I know this topic has been brought up a few times, but i had some specific questions. I have installed several 1783-NATR devices and they have...
Replies
0
Views
50
Hello We have installed several G.E. Fanuc 90 70 PLC Everything was ok but suddenly we can not communicate anymore with any PLC with the software...
Replies
0
Views
36
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
53
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
98
Back
Top Bottom