Allen-Bradley PanelView Modbus

Join Date
Jan 2018
Location
Najaf
Posts
1
I'm trying to build a project on PanelView C600 Touch Screen HMI. communicating it using Modbus with a PC via serial link. the PC act as a Modbus slave. after configuring both the slave simulating program and the HMI communication settings, I add a pushbutton command to the screen and linked it to a certain signal. when I run the project and press that command, the value of the register changed on the PC, but I got an error on the HMI saying "Write Error for Alias l63, Controller PLC-1, Address is 00001, Communication Flag is 0". Looking at the messages, it seems like the pc receiving the message and send its response to HMI but the HMI (master) couldn't receive or read the message, same thing happened with reading and writing all other data types.

Hope any one can help solving this issue.
Thanks in advance.
 
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/2711p-um002_-en-p.pdf
"PanelView Component/800: Write/Read Error for Alias xxx, Controller yyy, Address is zzz, Communication Flag is 0 ... This error can occur on a particular screen if the screen objects reference PLC data table areas which are not created, or some are created but not enough elements to cater for all the tag references."

What software simulation are you running on the PC to mimic the Modbus Slave?
Have you tried another software package?

Here are some other packages that you may want to try.
http://www.simplymodbus.ca/download.htm
https://sourceforge.net/projects/easymodbustcp/

Hope this helps you out.
Regards,
 

Similar Topics

Hi Having issues with a older PanelView touch not working. Screen is connected to a Desktop computer. screen used as a display with touch...
Replies
1
Views
110
Hello brothers We are contacting you because an error like [display change is currently controlled remotely] occurred while using the equipment we...
Replies
2
Views
203
Every time I power this unit up it loses its IP address and goes to DHCP . When I goto the config the IP address is 0.0.0.0
Replies
1
Views
729
Hello, I have several SLC-500 based systems. The user interfaces are PanelView 2711-TC1 touchscreens with firmware revision 3. I purchased a...
Replies
3
Views
2,037
i was trying to run a .mer file which i have uploaded from a running pvp1000 same model. when i load it on new pvp1000 it shows " the terminal can...
Replies
5
Views
2,236
Back
Top Bottom