Changing Controller Type in Logix5000
Lovell
Feb 2013
Saskatchewan, Canada
120
I am trying to use RSLogix 5000 to load a project into a processor that is different from the one in the program. I tried to change the processor type in the program but since the previous one has on board ethernet - it does not give me the option to switch to one without onboard ethernet.
Prev. processor:1756-L85E
Curr. processor:1756-L74
Any suggestions?
What software version are you running? There is a minimum version that supports the L8x controllers.
The manual says the L85E support starts at v28
Interesting ! I've been able to switch from ControlLogix to CompactLogix with embedded Ethernet.
I would approach it by exporting to *.L5K format, then creating a dummy project with the 1756-L74 and 1756-ENxT, and swapping out the Controller and root Network bridge module definition sections.
Thanks Ken, that worked - had to delete an Ethernet section as well since the port did not exist.
"CONFIG EthernetPort1(Label := "1",
PortEnabled := 1) END_CONFIG"
Hi all, I have an existing project and I am modifying it to my project since they are similar. I noticed the controller types are different. Is...
3,771
I have a half-prewritten PLC program supplied by a manufacturer that used real hardware. I want to download to softlogix virtual chassis to...
1,971
So we have this machine called a "quickwater" that we use to heat our low pressure water system. On the HMI screen there is a place where you can...
1,075
Hi all, Hopefully just a quickie here! We are trying to convert our controller type from an 1756-L71 to an 1756-L81E just to carry out a bit of...
3,945
I am working on expanding a control system for tanks, adding two additional ones. Each tank is represented by it's own equipment phase. The...
2,822