Prevent dust collection inside the enclosure

swapi1123

Member
Join Date
Jun 2022
Location
San Jose
Posts
1
We am planning to build an electrical enclosure on the manufacturing line. The only concern is to prevent dust from getting collected inside the enclosure. We will be providing with an pulsating airflow from the top of the enclosure to blow of the dust. With respect to the airflow, what are the things that we need to consider? What kind of air filter or pressure regulator do we need?
 
Are you planning on using an Exair unit or equivalent?
https://www.exair.com/n12cc.html

These systems come with or give recommendation of type of filter and pressure regulator.
If the cabinet stays at positive pressure, of even a few inches, you will be okay.

Don't think you need pulsating airflow, and it may be detrimental.
 
I would go with these
Thermoelectric Air Conditioners, cold plates, liquid chillers, Peltier coolers
First I would recommend you use a NEMA 4 enclosure even though it is inside the plane the NMA 12 will still leak
I would avoid any device that uses the plant air compressor air
Plant Air always has oil in the compressed air that oil will eventually end up coating all the components in the panel and make a real mess.
I have seen those used many times and they always end up with the oil and dust coating everything.
With the Teca units there is no outside air exchange so everything stays clean
 
I would go with these
Thermoelectric Air Conditioners, cold plates, liquid chillers, Peltier coolers
First I would recommend you use a NEMA 4 enclosure even though it is inside the plane the NMA 12 will still leak
I would avoid any device that uses the plant air compressor air
Plant Air always has oil in the compressed air that oil will eventually end up coating all the components in the panel and make a real mess.
I have seen those used many times and they always end up with the oil and dust coating everything.
With the Teca units there is no outside air exchange so everything stays clean

I have used a few Exair units. If filtered properly, no oil.
Thermoelectric is the way to go, but depends on heat generated in cabinet can make them costly.
It is okay for the Nema 12 to leak some as long as cabinet is slightly positive pressure.
If Nema 4 enclosure, you would not have to worry about dust anyway...
 

Similar Topics

Hi All, I am using a Micrologix 1100 to load various Jobs on a cognex camera. The way it works is that I send a command to load the file and I...
Replies
1
Views
1,524
We have L72 controller of Rockwell make with 4 nos. analog inputs from pressure transmitters. Due to break in cable connection OR transmitter...
Replies
7
Views
2,048
Hello, We have 5 floating licenses for Studio 5000. Despite training people to disconnect from the PLC and close the software, we still have...
Replies
6
Views
2,686
Hello, A few years back I was having a SLC 5/05 hard faulting, losing program, and requiring a download to get going again. The processor was...
Replies
7
Views
2,893
Hello All, In our facility we are utilizing an Allen Bradley Compactlogix controller. I am having trouble with maintaining tag values for...
Replies
3
Views
2,204
Back
Top Bottom