Hi there, very much new to AB Drives / Drives in general.

Driving a pump with SMC Flex Drive Rating: Pump (5-135) Revision 6.008.

Currently the drive parameters indicate:
Option Input 1 = Stop Option
Stop Input = Coast
Stop Time = 120

Stopping with this mode is causing issues as the back-pressure is causing the pump to stop instantly and hammering on the check valve.

The manual states that there are 'Soft Stop' and 'Pump Stop' modes, however I cant seem to find where I would set this?
(150-um008_-en-p.pdf pg14)

et2DpOYcib.jpg
 

Attachments

  • PMP085_Parameters.xlsx
    17.3 KB · Views: 9
Last edited:
Just out of curiosity, what is your process?

How are you stopping the motor? Are you sending sending 24V to terminal 16? Or using the .LogicCommand_Stop bit from the AOP?
 
What is parameter 32 set to, if it is set to soft stop then selection Stop Option for parameter 133 should enable soft stop.

I could be wrong...but I don't think parameter 32 is available with the pump configuration. I don't see it on the Excel printout.
 
On the SMC Flex, Pump Stop is an option module added to the starter when ordered. If you didn’t order it, you will not see the parameters for it. I can’t remember if it can be added after the fact.

The newer SMC-50 has everything built-in and you just enable it or not.
 

Similar Topics

Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
Replies
0
Views
299
Hi Everyone, Looking for a "Sanity Check" on my programming for Starting and Stopping a pump connected to a SMC-3 Flex Soft Starter via...
Replies
4
Views
2,447
I’m not a regular user of soft starts but the SMC Flex list the aux contacts can be set to “Normal”, what does normal mean? The manual doesn't say...
Replies
8
Views
4,997
I am facing a problem in which when the emergency stop is pressed, the motor comes to zero speed but going to start state instead of stop state...
Replies
0
Views
1,596
Hi, I have one SMC FLEX soft starter.When I connected to Power soft starter showing full output voltage even with out control Off.I am using...
Replies
17
Views
11,417
Back
Top Bottom