GE RX3I Analog Input card

jgunnels

Member
Join Date
Jun 2010
Location
Vancouver Washington
Posts
24
Hello All,

I am setting up a new RX3I test Rack with random I/O cards and a ( Horner ) HE693ADC420 analog input card. I do have a running system to duplicate and have setup the config the same way on this card ( see attached ). using a fluke current source I am not seeing any change on %AI0001,2,3,4 ? any ideas on this? Also I have swapped out the horner card with a new one just to make sure its not bad. Any Ideas?

Using Proficy 9.8 sim 9 rack is on a IC695CHS016 16 slot rack



Joe

Horner.jpg
 
The hardware configuration looks good. The wring diagram shows jumpers between terminals 5 - 7 for channel 1 (%A1001), terminals 6 - 8 for channel 2, terminals 15 - 17 for channel 3 and 16 - 18 for channel 4. Are those in place on your system?
When you applied the signal from the Fluke and got no response, did you try reversing the leads?
 

Similar Topics

Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
Replies
5
Views
96
I have a system using Rx3I CRU320 redundant CPU with Proficy Machine Edition Software. In the hardware configuration of each CPU module, under...
Replies
14
Views
376
Hi, we are using Rx3i CRU320 redundant PLC system and we noticed a discrepancy between Primary and Secondary controller. Couple of variables (DI)...
Replies
8
Views
270
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
Replies
1
Views
964
Hello all, First time poster, long time viewer of these forums. Could not find my solution on here. We have had issues with a Comm Fail on an...
Replies
2
Views
364
Back
Top Bottom