I have an SLC 5/04 with local I/O modules in its rack, along with a 1747-SN for some remote IO. The remote IO is flex with a 1794-ASB. The processor is using M0 & M1 tables to retrieve some data from the 1747-SN (thinking about it I'm not exactly sure what, as the RIO shows in the I and O tables).
I am now wanting to add a modbus scanner card prosoft MVI46-MCM to communicate with a crowcon vortex gas detection panel that has been installed. I have read the manual for both the vortex and MVI46-MCM. This module also needs to use the M0 & M1.
I think i already know the answer to this but can an SLC have two speciality modules in the same rack?
If not what other options do i have? Unfortunately the way our system engineers are Ethernet is not really an option.
CH0 DH+ is used for comms to PLC 5 and the site SCADA.
CH1 DF1 is used for comms to PVP700.
Yes it can have multiple. I have a system with 4 SN cards and a Modbus card. Your only limitation is 256 words of Inputs and 256 words of outputs. Also there are some limitation on M files in each scanner card, but that is only for using block transfer to analog type modules.
Hi everyone. I am new here in this page. This is my first post. I hope to receive the best suggestions and tips wanting also to collaborate...
2,611
I have a few SLC racks and modules. These are free to good home, pick up or you pay shipping. See pictures.
1,439
Has anyone used the AB IFM Terminal Blocks and cables with ControlLogix TTL I/O modules. AB says that they do not support the IFM wiring system on...
4,228
Has anyone seen this before. I have started working on a SLC 5/03 that cannot see any of the i/o modules it a 7 slot rack. When I do a READ...
3,810
Dear Experts, In SLC-500 CPU using Control Net Scaner 1747 i am trying to shedule the remoter I/O. while auto scaning it genarate default scane...
3,750