Controlnet PF-40P Drives

trueninjalo

Lifetime Supporting Member
Join Date
Oct 2015
Location
Ohio
Posts
40
Hello staff,
I have a drive network of 16 Power Flex 40P drives on control net and 8 PF525 on ethernet ring. Maintenance states one of the 40P drives (node 10) failed. After replacing the drive, the next drive in line (node 11) failed. After replacing that one, the next one (node 12) failed. Has anyone seen this before? This is the information passed to me and I am sitting here thinking the drives may be functional but there is possibly something with the network that's causing the failures. A couple weeks ago I had to rename some drives and rescheduled the network as we added an Ethernet group of drives in the middle of the conveyor line. The lines have been running well until last night.

Thanks in advance,
Anthony
 
>we added an Ethernet group of drives in the middle of the conveyor line.

How exactly did you configure those in the I/O tree of the controller ? The network interface must be in the chassis with the CPU (1756 ControlLogix) or integrated with the CPU (CompactLogix).

This will work:

Controller -> ControlNet Bridge Module -> ControlNet -> Drive.

And this will work:

Controller -> EtherNet/IP Bridge Module -> Ethernet -> Drive

But this will only work by coincidence or until the buffers get interrupted:

Controller -> ControlNet Bridge Module -> ControlNet -> ControlNet Bridge Module -> EtherNet/IP Bridge Module -> Ethernet -> Drive
 

Similar Topics

Hello all. Been reading for a long time, 1st real post. AB was unable to help me beyond "Yeah, that's old, we think you should upgrade..." which...
Replies
4
Views
2,343
Does anyone know of a cheap USB to ControlNet or USB to DeviceNet adapter (I'm looking for both). I thought PLC Cable would have one but I did not...
Replies
16
Views
2,201
I'm having an issue trying to backup a ControlNet network. Within RSLogix5000, when I click on Module Properties of the 1756-CNB (Rev 5.001), the...
Replies
2
Views
802
An issue occurred at an organization here in whereby the ControlNet card developed a fault. Card Details: Catalog/Series; 1756-CN2RXT B Part No...
Replies
0
Views
422
Hi, We have ControlLogix installed at my plant with Flex IOs communicating with controller through ControlNet module. Yesterday, while controller...
Replies
0
Views
460