Hi, I have problem with Aentr and compact logix sistem:

1769-L32E ethernet
1734-AENTR Adapter

Set ip adress with Bootp_dhcp.
I see the aentr on linx, ping is ok but on I/O configuration the module has error (connection time out). All the led (aentr) are green only the network status flash green every 20-30 sec.

I try to reset the module but the problem persist
 
What revision is all your hardware at? I just started researching installing one of these and the 6th page of the manual outlines what revisions are necessary.

If using the adapter with a 1756-ENBT module, 1768-ENBT module or an L3xE processor, use the following required firmware versions for these bridge modules:
If you use the BootP utility to assign IP addresses to the adapter, use version 2.3.2 or greater. • 1756-ENBT firmware version 4.5 or greater • 1768-ENBT firmware version 2.1 or greater • L3xE processor firmware version 17 or greater

http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1738-in028_-en-e.pdf

I'm looking to see if I can use one of these to connect a Micrologix 1400 to Controllogix5000 so please post up how your install has gone.
 

Similar Topics

We had recently upgraded Rockwell control system from ControlNet to Ethernet (1719-AENTR). and in last couple of months 2 different AENTR devices...
Replies
3
Views
150
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
1
Views
111
Hello all. I have a remote that uses a 1734-AENTR series C. We had to change it to a new one and, after adjusting the IP and number of slots...
Replies
16
Views
451
The issue we have is that the IT2I thermocouple card and the RTD temperature sensor card connected through a point IO AENTR is constantly trying...
Replies
12
Views
475
Hi guys, I have just recently purchased a 1734-AENTR module so that I could learn how to configure it through LogixDesigner and establish comms...
Replies
1
Views
280
Back
Top Bottom