Old March 1st, 2018, 02:09 PM   #1
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,739
Automation Direct DL05 and DirectSoft

Hello everyone, I have a customer that needs some help and I dont really understand the question so im posting it here, I think he is over thinking the problems

Quote:
I’m stuck because I do not fully understand how the ON/OFF for outputs really work.

For example, I wrote a rudimentary program to mimic the operation of a traffic light that controls a North/South and East/West intersection. My process is simple:


Start:

Green_North (Y0) and Red_East (Y5) = ON

After TMR A reaches 100,

Amber_North (Y1) and Red_East (Y5) = ON - - Green_North (Y0) = OFF

When TMR A is between 100 and 200

Red_North (Y2) and Green_East (Y3) are ON - - Amber_North (Y1) and Red_East (Y5) are OFF

And so-on until the cycle repeats itself.

Obviously, I’m in the “Cycle 2” hell. The scan of the process is seeing lights turn on at the start of my ladder and then seeing them turn off later in the ladder so when the output actually starts, the initially set lights never come on.

How do I fix this condition? Would “Immediate” output instructions work or is there a better process?
I have asked him for the logix he has made to date and will post once he shows it to me
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old March 1st, 2018, 02:19 PM   #2
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,567
It sounds like a clear case of multiple coil usage.
  Reply With Quote
Old March 1st, 2018, 02:22 PM   #3
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Cobourg
Posts: 2,611
http://accautomation.ca/building-a-p...oud-of-part-1/

The above thread may help him out. It was written in the Do-More but can be easily adapted to the DL line.
I think his logic may be off. The traffic lights should start RED/ RED etc.

Regards,
__________________
Garry
https://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
  Reply With Quote
Old March 1st, 2018, 03:28 PM   #4
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,739
Thanks guys, he is going to join the site so he can chime in once he can log in
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old March 1st, 2018, 03:35 PM   #5
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,739
I'm on my phone so I can't look at it but anyone wants to help I'm attaching the logic he zipped up

Thank you
Attached Files
File Type: zip Don_Traf_Lights.zip (5.2 KB, 12 views)
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old March 2nd, 2018, 06:40 AM   #6
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,739
On the road this AM so I still cant help much, anyone look at the file? below is a email from him, he has also registered on PLCTalk but he can not post yet

Quote:
Mark,

I am an electrical instructor. The class I have starting on Monday is a PLC class but my focus is “What to do when the customer calls the electrician.” I have a lot of programming experience from my days with IBM, but that is with full blown programming languages.

I’m trying to get my arms around programming so that I can effectively write code that will give the students the appearance of hardware failures so that they can go through the panelboards that we have set up and test for hard failures.

The last teacher left very suddenly, and the class fell smack dab into my lap.

Thanks for your help
I will try and look at the logic once I get back if no one else can
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old March 2nd, 2018, 07:54 AM   #7
Bob Mattos
Lifetime Supporting Member
United States

Bob Mattos is offline
 
Bob Mattos's Avatar
 
Join Date: Nov 2013
Location: South Carolina
Posts: 27
There seems to be a few things on quick glance. For example, what happens between 100 and 200 on the timer? I was going to put it into an 05 and simulate on an HMI and see what it does but haven't had the chance yet. This is the whole program. Rung 6 is end coil.
Attached Images
File Type: jpg Capture.jpg (44.6 KB, 101 views)
  Reply With Quote
Old March 2nd, 2018, 08:20 AM   #8
AustralIan
Member
United Kingdom

AustralIan is offline
 
Join Date: Jan 2013
Location: UK
Posts: 772
Yeah, you are using the programming logic that you would in the 'full blown' languages, where you list every possible input combination and define the outputs for those. ie.

Code:
if case1
  Output1=false
  Output2=true
Else if case2
  Output1=true
  Output2=false
Else
  Output1=false
  Output2=false
In ladder, a partially blown language, clarity is achieved by having all the logic for what turns on an output on the one rung. This is equivalent to writing this in full blown languages.
Code:
output1=case2 AND NOT case1
Output2=case1
You can see that both code snippets above give the same outcome.

In ladder we write this as

Code:
case2 case1 output1
-][----]/[----()

case1 output2
-][-----()
I hope you can extrapolate to your situation.
  Reply With Quote
Old March 2nd, 2018, 08:24 AM   #9
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,567
As I suspected, multiple coil usage. A common mistake by programmers new to PLC ladder logic, especially when the come to the field with experience programming in other languages.
In rung 2, instead of the coil addressed to Y0, use a coil addressed to C0.
In rung 3, instead of the coil addressed to Y0, use a coil addressed to C1.
Add an additional rung with a coil addressed to Y0, controlled by C0 OR C1.
Do something similar for Y1, Y2, etc.
  Reply With Quote
Old March 2nd, 2018, 08:31 AM   #10
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,739
Thank you for the replies

After looking at it... yes same output used several times as Steve pointed out

Bob, Yes I think this is as far as he has got... I see a long weekend for him

AustralIan, I think Don needs to pull out his Electrician hat and put the programmer one in the drawer

I have asked him to call me and I will update if I hear back

Thanks again
Mark
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old March 2nd, 2018, 11:57 AM   #11
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,306
Is this a real world application or a lab for school?? Do they use DL Processors for Traffic Light control?
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old March 2nd, 2018, 12:10 PM   #12
don.farr
Member
United States

don.farr is offline
 
Join Date: Mar 2018
Location: Tidewater Virginia
Posts: 3
Classroom environment only

I all and thank you.

I'm finally allowed to post and respond. My goal here is to write this control program and get it operational. Once I have that completed, I am going to put hard electrical failures on the workstations and have the students trouble shoot the electrical failure, such as a relay with a blown coil so that it cannot pick.

However, until I get this program off and running I'm dead. I have until Monday of next week but that can slide as I have a lot of electrical items to cover before I hit this little beastie.

Pointers are gratefully accepted. Fingers pointing to documentation are also greatly appreciated. I don't mind doing the legwork especially since I will benefit from the knowledge.

Don
  Reply With Quote
Old March 2nd, 2018, 12:22 PM   #13
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,739
Hi Don,

Their user manuals have saved me several times

https://cdn.automationdirect.com/sta...ectsoft6m.html

Did you buy one of my trainers? if so there are lessons that came with it on the flash drive
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old March 4th, 2018, 06:42 PM   #14
don.farr
Member
United States

don.farr is offline
 
Join Date: Mar 2018
Location: Tidewater Virginia
Posts: 3
I'm having fun being a functional idiot :)

I rewrote the sample program using Control Relays as suggested earlier. I'm not at the school and won't be there until 18:00 tomorrow evening so I have no way to test what I just programmed.

If anyone could please unzip the file and run it against a DL05 or just read it and tell me what I am doing incorrectly and how I can fix it to make it work.

Don
Attached Files
File Type: zip Control_Relays_Traf_Lght..zip (4.1 KB, 2 views)
  Reply With Quote
Old March 4th, 2018, 08:34 PM   #15
Bob Mattos
Lifetime Supporting Member
United States

Bob Mattos is offline
 
Bob Mattos's Avatar
 
Join Date: Nov 2013
Location: South Carolina
Posts: 27
Still not right

As was pointed out, AD doesn't work well with multiple coils. You still have your timer not consistent. I made a few quick changes and simulated it on an HMI and my changes worked ok. I wouldn't use it with real traffic but it stays along the way you were thinking, I think. (if you just load my program in, you'll need to change the C3 back to X3. It was just easier on the HMI)
Attached Files
File Type: zip Donslights Rev.zip (4.2 KB, 3 views)
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
DL05 Directsoft V-Memory Access OneDeadPixel LIVE PLC Questions And Answers 3 February 5th, 2014 10:24 AM
Direct Logic jwtdjt LIVE PLC Questions And Answers 14 February 22nd, 2007 10:58 AM
Staging in DL05 w/ DirectSoft powermonkey LIVE PLC Questions And Answers 5 August 8th, 2005 03:42 PM
Problem with DirectSoft RDay LIVE PLC Questions And Answers 5 October 21st, 2003 03:27 PM


All times are GMT -5. The time now is 08:58 AM.


.