Hello,

I have a DC motor wit below specs. We need to test run it but. We have a transformer and a recitifier that can provide the DC voltage and current. However we have no start resistance. Is it possible to start anyway? If not how to calculate start current?

kW 4.0
Rev/min 1500
Arm Volts 110
Armature Amps 41.6
Field Volts 110
Field Amps 0.55
Wound Compound

NOTE:
Resistance start required. Starter not of our supply
 
I would use either 2 transformers & rectifiers or a transformer/rectifier for the field and a lower voltage for the armature to start and test, or even a car battery for the armature to test...

The Locked Rotor Amps (starting current ) of the armature will blow up a power supply rated too low with a full-voltage start. The armature resistance is likely < .25 ohms, so figure 110v/.25ohm= 440A!
 
41.5 amps ate a lot for a 110 volt motor
the other odd thing is that most DC motors are rated at 90VDC the rectified 110 vac
that beaing the motor start inrush of that motor could be 10 X the full load rating
more than likley it would exceed 200 amps you power supply would need to supply at least that.
A resistive start means you need to put a resister in series on start up to limit the inrush
current
what you really need is a DC drive sizes correctly I would think you client could be able to supply you with the one they are using so you test the project.
 

Similar Topics

How to fix if appears code “$115 plc-restart running” on the screen OP17
Replies
3
Views
132
Hello everyone, I'm new here. First of all I just want to say that you guys are very knowledgeable and reading your posts on here has saved my...
Replies
4
Views
159
can anyone has a good program to learn plc programming online. i have the basic looking into improve my skills thanks
Replies
1
Views
137
Hi guys! I'm working in Studio 5000 and have a bunch of armorstarts there (+- 40). I need to set up parameters for each of them, mostly just same...
Replies
0
Views
90
Hello I am trying to make a program work with a sqo instruction .The process has 5 steps ,and a starting step of zero.There should be 8 sec...
Replies
17
Views
1,033
Back
Top Bottom