Hi Gents,
I've been asked to install a remote IO panel with a HMI onto an existing plant on a site. I know the remote IO will be fine to integrate, but I have been told that the project only ever allowed for a PV800 HMI. The question I have is will this HMI work on the plant PLC? See details below:
HMI - 2711RT4T
PLC - 1769-L32E (CompactLogix5332E)
Revision - 20.12
The documentation I have found is not clear cut if it will work with this range of controllers and from what I can find in CCW, you can only select a L1 controller as a CompactLogix device.
Any help would be appreciated if you've dealt with this before.