GE Fanuc CPE305 issue
rahmanjr
Sep 2016
johor
Hi All. Good Afternoon.
Today i'm facing 1 issue with my GE Fanuc PLC.
I'm found my CPU was death during startup.
I'm change with spare CPU and download the backup program but the PLC go to fault status.
Attach picture original CPU and new CPU also the fault table.
Thank you in advance for those are helping me on this thread
Double check your hardware configuration. There are discrepancies between what you declared in the software and what is actually present in slots 3, 4, 5 and 6. There is also something about the module in slot 7 that the configured CPU doesn't like.
Your new CPU is newer than the original. That is not likely to be the cause of your problems.
What Version and "SIM" of Machine Edition are you running?
The CPE305 recently had a firmware change that takes a new SIM for ME...
Don't forget to remove the "isolator" from the battery on the replacement CPU. It will not effect configuration issue, but no real time clock.
Hi Steve Bailey. thanks for you reply. Today i'm checking 1by1 all the configuration also compare with my others backup found all match and correct. But finally i found the actual root cause, my last 2 unit analog output was faulty (slot 8 & 9). After disconnect this 2 unit my CPU back running. Unfortunately i have only 1 spare card in handšŸ˜“šŸ˜“
Hi NetNathan. I'm using PME version 8.0.
What you mean with "SIM". Sorry because i'm only beginner on this GE Fanuc PLC.
Battery isolator already removed before i'm slot in to rack
You did not include enough of the screenshot to show the timestamp of the faults. It is possible that they happened a long time ago and were no longer relevant. Once a fault has been entered in the fault table that entry will persist until cleared.
Original CPU was death. That why i can't retrieve the data or error code. When i'm replace to new cpu this 5 alarm come out. I'm not suspect my analog card faulty because from fisically the card look good. LED indicator still ON.
I know Once again I may be sailing in Uncharted Waters but thought I would throw it out there anyway. I have a Emotron TSA52-450 Soft Start with...
5,591
I have a RXC3I with IC695CPE305 and IC695CHS012 Universal Backplane. The problem is the analog cards. I am Using the IC693ALG221 analog current I...
6,321
I have a CNC cutting equipment, all the components are Fanuc from the CNC CPU A02B-0307-B822, a PLC AIF01A and a panel i, on the panel i (operator...
108
I want to buy this program if anyone has it. Absolutely no one has it officially for sale. My cpu is IC610CPU104B My mail...
109
I've got a Micrologix 1100 with ethernet and I'm trying to configure communications to a Fanuc R30iB controller. I'm pretty sure you have to set...
101