Hello.
I'm mounting a Sarco Spirax Flow Meter going to a Red Lion Data Station Plus. From the DSP we are going to a Compaq logic controller. This is a first for me. From the flow meter to the DSP we are using RS485. The flow meter has a Mod Bus A and B terminals going to an Rs485 port. The print shows twisted pair. Any ideas on what lands on A or B?

Also. Does the red lion get added to the I/O tree in PLC program? Any info would be much appreciated.
 
This is erroneously posted in the 'practice posting' area. Maybe the moderator will see it and move it to the Q&A.

I can help a little on the flow meter side.

The flow meter is a Modbus RTU slave that talks over an RS-485 network link.

The DSP has an RS-485 port which needs to be a Modbus master in order to talk to the flow meter slave.

If the flow meter has only A and B connections, that it is "2 wire" RS-485. The port on the DSP is an RJ45 that is '4 wire' RS-485, but the DSP manual shows how to jumper terminals to make it "2 wire".

Usually line A on one device connects to line A on the other device. But the EIA standard does not define A/B so some vendors define it one way, others the opposite. If you have comm problems, a classic test is to swap A and B on one end and see if that makes it work. Connecting the lines backwards will not damage the drivers, but comm won't work.

When you configure the DSP's RS-485 port as a master so that it can communicate to the flow meter, It can also separately write to the PLC, if the PLC supports Modbus RTU as a slave. You'll have to check into that.

The protocol (Modbus, DH+, whatever) that the DPS and the PLC use have to match, just like the hardware transport layers have to match (RS-485 on both sides, or RS-232 on both sides, or Ethernet on both sides).
 

Similar Topics

Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
110
Dear All, I need a sample PLC program to count the output pulse of a mass flow meter so that a specific amount of mass (for example 100gm)can be...
Replies
2
Views
139
Morning Guys, I am installing a turbine flow meter with a pulse output to measure flow on a compactlogix 5069 -L306ER through a 1734-VHSC24...
Replies
3
Views
1,580
I need modbus communication tool for Yokogawa Rotamass Flow meter? can any one help me.
Replies
1
Views
978
Hey everyone, I was on a customer's site on friday where they have a large bioreactor that they bought secondhand from a previous user. System is...
Replies
22
Views
4,425
Back
Top Bottom