1734-OW4 Leakage current
Jason P
Jan 2006
Burlington
22
Just looking at the manual for 1734-OW4 and it states its "4 type A Normally Open electromechanical relays" but right below it there is a spec for leakage current 1.2mA...? Why would a mechanical relay have a leakage current spec?
Do you mean the 1746-OW4?
the manual I have shows 0 ma leakage. See pdf.
Can you post what you are looking at?
Scott: That "solid state equipment differs from electromechanical equipment" reference to publication SGI-1.1 has been in Allen-Bradley user manuals since the 1980's. It is a universal technical disclaimer and does not give any information about the specific device.
Jason: The leakage is through the snubber circuit that's built in to the module to protect the relay outputs. It leaks about 1.2 mA at 240V, and about 0.6 mA at 120V AC.
RA Knowledgebase 39709 explains how to size a bleeding resistor if your load cannot tolerate the AC leakage.
Just curious about something. This card is a 4 point relay output card so it only has 4 outputs. But in the Controller tags when you look at that...
1,692
422
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
224
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
344
Hi all, This is my first time working with a 1734-IE2C analog module. I am tasked with wiring the flow meter into the analog card and the OEM is...
163