All thermocouples will give readings outside of their stated "range", which is just a "usable" range where the temperature to induced voltage is "most linear".
If you are only going a few deg.C below 0, then I don't really see a problem, except that the reading will be *marginally* inaccurate.
As well as that, the sensor head will most likely NOT clamp the output signal to 4mA/20mA, they usually allow +/- 5 to 10% under and over the stated "range".
And on top of all that, most PLC analog inputs also allow a %age under and over "range" of +/- to to 10%, so that going outside the "range" produces correct values.
And don't forget that the math done in the SCP is just a "straight-line" relationship, and it will scale the input value to an output value anywhere on that straight line, even if the input value is outside the stated Low and High input parameters.
The only problem I can see is if the sensor head is configured as a 0 to 20mA signal, because you just cannot go below zero current ...
The other thing I can see is that that SCP_RD provides two output values, one as a REAL value, and one as a DINT value. But it gives the DINT value as having an implied 1 decimal place, so the 13 is really 1.3, an approximation of the 1.2817774 coming out of the REAL parameter.