I have pulic network of PLC
every PLC as local network with local devices,
I have one PLC with EN2T card that allow me to connect to the local devices from the pulic network throw RSLINX,
my qustion is:
I want to connect to the Panel view with VNC, but witch IP should I write?
the IP 10.**.168.103 is the IP of the PLC
and the local panel view IP is 192.168.1.101

1.jpg
 
I can reach to 192.168.1.101 only throw RSLINX
my PC IP is 10.**.168.**
how I can I reach 192.168.1.101 without RSLINX?
 
You will need to do traditional routing such as adding a NAT to be able to accomplish what you want. CIP bridinging from one device to another only works with CIP connections, so you can't bridge from one EN2T to another except with RSlinx or similar applications that use CIP.
 
.

You will need to do traditional routing such as adding a NAT to be able to accomplish what you want. CIP bridinging from one device to another only works with CIP connections, so you can't bridge from one EN2T to another except with RSlinx or similar applications that use CIP.

which device you are recommnad? for doing the routing?
 
Buying a license of RSView ME Station (or whatever they've changed the name to), copying the HMI projects and modifying the controller path might be easier than ruining the network segregation you have going.
 

Similar Topics

So I have code to read the IP address of a 1756-EN2T with a MSG block - Get Single Attribute. Does anyone know where to find the MSG block...
Replies
12
Views
1,069
I've been trying to get this Ethernet module configured to send emails to our relay server but cannot get it to work. the EN2T is running...
Replies
7
Views
1,714
Dear All, I have been using 5561 CPU with redundancy, Few days ago, I have seen the message Disqualified on RM module of secondary PLC. and i can...
Replies
1
Views
730
Good day folks, We have an L71 processor (v30.02) in a rack with an EN2T connected to the plant network & another (v10.007) used for IO only -...
Replies
2
Views
2,098
I have a pair of 1756-L73 controllers on A4/A backplanes with PA72 power supplies, configured for redundant operation with RM2 and EN2T modules...
Replies
1
Views
2,729
Back
Top Bottom