Siemens S120 Servo parameter to PLC

JDCROCKETT724

Member
Join Date
Jun 2010
Location
Michigan
Posts
249
I am using an S120 Servo with Telegrams 30,105, and 750. This is all working. The question is how do I get the motor temperature (Parameter r35) to the PLC. I setup a free telegram for 1 word on the hardware of the PLC, but I don't know how to tie r35 in the drive parameters to pass that along to my free telegram. :confused:
 
I am using portal. I think I found it. I had to tie the r35 motor parameter to p2051. I was confused when I saw the drop down with all the PZD's, but found that my 105 telegram was using the first 10 PZD's and my 750 was using PZD 12. I found from my free telegram configuration on the PLC side in the network configuration that it was assigned to PZD 11. So I tied r35 to PZD 11 in the drive configurations and boom. It worked.
 

Similar Topics

Hi all, I am having a machine with old 802d sl siemens controller. I am trying to tune servo by Siemens starter software. Anyone experienced...
Replies
0
Views
64
Hi Everyone, I am new to siemens servo drives, needs some helps and wondering if you can help me. The machine has Siemens S120 Servo Drvie and...
Replies
2
Views
1,632
Hi, I'm programming an S120 servo indexer with s7 classic and wondering if the best way of doing this is with Easypos? Or is there something...
Replies
4
Views
1,971
Kindly, has anyone tried to control Lenze servomotors with Siemens S120 drives ? Any special hints ? Have some concerns for the resolver and servo...
Replies
5
Views
217
Kindly, can we install new Siemens Sinamics S120 motor modules and new 1FK7 servomotors, in place of old types ? Will the old motion control...
Replies
0
Views
1,104
Back
Top Bottom