Old June 19th, 2004, 05:00 PM   #1
shady_yehia
Member
Egypt

shady_yehia is offline
 
Join Date: Jun 2004
Location: Cairo, Egypt
Posts: 30
Question Siemens S5 135U Peripheral I/O Addressing in OPC Server

Hi there.. I'm building a SCADA application with an old Siemens S5 928-135U plc.. i'm using an OPC Server from SoftwareToolBox..

The proplem is that all addresses of the analoge channels of the plc are in the Peripheral I/O area (e.g. TPW128,TPW130) and so on. But the OPC Server doesn't support these addresses. can any body tell me what to do?

Thanks in advance..
  Reply With Quote
Old June 20th, 2004, 11:10 PM   #2
andybutcher
Member
Australia

andybutcher is offline
 
Join Date: May 2004
Location: Brisbane
Posts: 52
You could try moving them into a data block?
  Reply With Quote
Old June 21st, 2004, 05:19 AM   #3
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,302
/agree Andybutcher

Create a "shadow" data block or two, and reference that from your SCADA system.

In the PLC logic, copy all of your Periperal inputs to an "Input Shadow DB (area)", and copy your writes from the SCADA System from an "Output Shadow DB (area)" to the actual output words.

As a general rule, I do that with almost all of our SCADA/PLC systems; that is, never refer directly to any physical I/O area from the SCADA system. I've never considered it a good idea especially to have an external device writing directly to my output tables.
  Reply With Quote
Old June 22nd, 2004, 06:25 PM   #4
shady_yehia
Member
Egypt

shady_yehia is offline
 
Join Date: Jun 2004
Location: Cairo, Egypt
Posts: 30
It is a great idea.. I'll try it out and tell you the results..

Thank you guys..
  Reply With Quote
Old July 11th, 2004, 02:13 PM   #5
shady_yehia
Member
Egypt

shady_yehia is offline
 
Join Date: Jun 2004
Location: Cairo, Egypt
Posts: 30
Thank You Guys for your help last time.. But another problem just came on the way.

I'm reading all tags very well, but i can't write data to any memory adderess in the data blocks or the flags area. why is that?

remember that i'm using the AS511 Programming port protocol and an OPC server from softwaretoolbox.
  Reply With Quote
Old July 14th, 2004, 09:02 PM   #6
andybutcher
Member
Australia

andybutcher is offline
 
Join Date: May 2004
Location: Brisbane
Posts: 52
I am not sure about this as I have only used OPC to read data from a PLC. Are the tags you are reading defined as read/write or are they defined as read only in the OPC server software? This maybe the problem. Another thing, if you establish a new tag and you write to it using the scada, do you see the changing status of the bit or word in the PLC?

Andrew Butcher
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens CP1613 with OPC Server on SR protocol budtse LIVE PLC Questions And Answers 0 December 24th, 2004 11:03 AM
Need help on siemens OPC server! TEOWK LIVE PLC Questions And Answers 3 November 3rd, 2004 04:13 AM
SIEMENS OPC Server TEOWK LIVE PLC Questions And Answers 1 November 2nd, 2004 02:47 AM
OPC Server for Siemens and Ethernet Prince LIVE PLC Questions And Answers 8 August 24th, 2004 07:52 AM
Two 135u in one S5 SIEMENS PLC ayman metwally LIVE PLC Questions And Answers 3 March 19th, 2004 05:43 AM


All times are GMT -5. The time now is 07:24 PM.


.