PVPlus 7 not trending historical data

phuz

Member
Join Date
Jun 2008
Location
Mohnton, PA
Posts
1,044
I've setup everything as I have in the past, and re-read the tutorial to make sure I didn't miss anything, but my PVPlus isn't trending any historical data.

Data log is setup for appropriate tags, and enabled in the startup. Trend object references same tags for the pens and calls the Data Log Model associated with those tags.
 
Phuz,

Make sure your trend screen is never closed or replace and is always running in the background.
 
That's not true at all. When using a data log, you can 100% close the screen and come back to it.

I tried "Delete Log Files" when transferring and now it seems to be trending, although I found a bug within this. I have a tag that is in the data log called "Shifts" and in my trend object my pen uses an expression "Shifts * 25" and when the trend is re-opened, it does not show any historical values. If I remove the "* 25" from the expression, it shows "Shifts" just fine.
 
I had a Rockwell contractor setup trends for me in the past. He was absolutely convinced that you needed an SD card (at the back of the HMI) in order to log the data. Although based on the documentation, you should be able to store data without it, I haven't dug that much into the manual.

All that being said, if you find a good guide on how to keep your data log, I would definitely be interested for some of my own applications.
 
I had a Rockwell contractor setup trends for me in the past. He was absolutely convinced that you needed an SD card (at the back of the HMI) in order to log the data. Although based on the documentation, you should be able to store data without it, I haven't dug that much into the manual.

All that being said, if you find a good guide on how to keep your data log, I would definitely be interested for some of my own applications.

You can log to the panel and run a BCD to copy paste to a USB, or you can also log to a csv on a network drive, or USB, which doesn't require any input.

Decent guide: https://theautomationblog.com/datastore-plus-step-by-step-setup-in-factorytalk-viewstudio/
 

Similar Topics

Hello, I want to make touchscreen push buttons invisible based on certain conditions. When these conditions are true, these buttons will become...
Replies
1
Views
986
So I've got an issue I have yet to figure out. I have a PVPlus standard HMI runtime v12. I've gone into the system and set the date and time and...
Replies
7
Views
4,807
Hello all. Sure hope someone can help with this. I have a system down because it is dependent upon its PV1000 and operator inputs to run it. I had...
Replies
6
Views
1,592
I'm looking to use a second monitor as a data display for a customer. I know the FTVP is available but would like to actually duplicate the...
Replies
4
Views
2,144
On all of my PVplus 700's; once the download is complete, the HMI restarts with the new .MER file. On my 600, I have to exit to configuration and...
Replies
3
Views
1,491
Back
Top Bottom