AB 1734-AENT POint IO issue
ettikudiappan
Apr 2002
Singapore
131
We are facing a point IO communication issue intermittently, once in 3 days. While running, the Network Status LED turns flashing red and the Point Bus status LED turns solid red. This is a symptom of wrong configuration of the number of ASCII modules connected to the point IO, but if this were the case the Point IO should always fault.
I changed the Point IO module itself (1734-AENT), the problem occured again. Then we changed the power supply, also same issue.
The Point IO has 5 modules connected to it, 2 RS485 and 3 RS232 modules. The RS485 modules are not used.
Anybody else faced the same issue? We have other POint IO in the plant that work perfectly well.
Hello. My facility has Point IO modules (on a separate cabinet) which is connected to a controllogix PLC via 1756-EN2T module. We lost...
1,402
Hi, I just bought a 1734-AENT Series C module (Revision 6.01). I am using RS logix5000 and at site we have a running system with control logix...
16
8,798
Hey guys, got a little situation here which i am not sure if its something viable. We are using a 16 slot chassis with 7 IB8 input cards and 8...
1,798
Currently have an Allen Bradley 1734-AENT (CIP Ethernet) Module, with 2 points of IO. In the first slot is a 1734-IB4 (4 point Input), and in the...
4,892
Hi, I am adding a 1734-AENT with (3) IB8, (1) 1734-FDM, (1) OB8. In my software I only have 1734-AENT/ A available. The card I bought is series...
2,572