FX1-48MR stopped during power cycle

Edwinsky

Member
Join Date
Apr 2005
Location
Pasig CIty
Posts
34
Hello.
I've just purchased a used Mitsubishi PLC FX1-48MR from a surplus store. During testing I've noticed that when power was cycled, PLC goes back to STOP. I cant find a RUN/STOP switch on it. Is there hidden inside? I can only run it on sofware. Is it defective or I have to do something? There is no error. I have previous experiences on FXon/FXos & FX2n, first time to encounter FX1. Please help.

Anybody knows where can i download manual for this PLC?

Thank you.

Edwin
 
On this model the RUN condition is from an INPUT. You will find it near the AC power connection terminal... look closer it says RUN :)
 
Go HERE to download any Mitsubishi manual you need.

In the pull-down, select "Industrial Automation". The remaining selections you can probably figure out.

🍻

-Eric
 

Similar Topics

Hello, I have a question on my HNC electrical and electronic engineering assesignment which has me stumped after hours of looking through PDF...
Replies
2
Views
2,566
0 -|X0|---------------------------------[MOV k0 d0]- 6 -|M8|----|T0/|----------------------------(t0 k5)- ............|--|T0...
Replies
14
Views
4,530
Hey! I have a transistor output FX1 14MT and I can't figure out how to wire it. (One of these...
Replies
2
Views
1,838
Dear all, hi to all PLC experts! I am trying to connect to proface HMI with my mitsubishi FX1s PLC but always failed to connect. the HMI manual...
Replies
2
Views
3,115
Dear all, hi to all PLC experts! I am trying to connect to proface HMI with my mitsubishi FX1s PLC but always failed to connect. the HMI manual...
Replies
0
Views
3,309
Back
Top Bottom