Hi!

I am a bit confused regarding a safety relay from Allen Bradley. We have a 230VAC model. I can't find what voltage there is supposed to be on the safety input? Acording to the wiring diagram in the manual it seems like it is the same as the voltage input, 230VAC (or 24VDC if you have a 24VDC model). But when I meassure I get 34VDC, this also seems a little bit odd to me. Anyone has any inputs on this?

The two channels are from S11 and S21.

Here is the manual link: http://literature.rockwellautomation.com/idc/groups/literature/documents/in/440r-in060_-mu-p.pdf

/Tim

SafetyRelay.jpg
 
It does look like S11 and S21 are 'connected' to Supply (A1 and A2) doesn't it?...:unsure:

The Minotaurs are pretty old relays, however, I don't believe, ever, a Safety Input will carry Line voltages, especially 230 VAC.

Even the 24 VDC models do not carry voltages over their Safety Input circuitry but proprietary pulse signals which will show up on a scope but not on an ordinary meter; EStop Safety Input circuitry is usually troubleshooted against required continuity over the relevant Safety Input circuit.

I am usually following the manufacturer's Wiring Examples:

Untitled.jpg
 
The safety inputs are 24vdc regardless of the units supply voltage if memory serves.

Edit: Check out technote 34783, better wiring examples.
 
Thanks alot for this clarification!

Yes I wire according to the manufacturer ofcoarse but I need to wire the correct colors aswell :)
 

Similar Topics

Hello, I am having to go old school on a project at work and I am having a major hair pulling event...help please!!! What we have is a 150 ton...
Replies
5
Views
3,726
After some interesting conversation regarding the safety of emergency stops, I saw some posts talking about the safety standard conversation...
Replies
16
Views
172
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
106
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
103
Hi I have a yaskawa gp7 robot arm which I am going to use for machine tending with a cnc mill. Is it a good idea to buy a SICK laser scanner for...
Replies
5
Views
234
Back
Top Bottom