Steps toward my first real world PLC project (Conveyor system)

Good Morning Everyone,
I am entry level PLC programmer and this is going to be my first PLC project at my company. I would like to thank you for this forum and people who helped me to gain some knowledge. I need few things to ask or correct me if I am wrong to finish this project.

Today, we just got the control panel installed and electrical guy power up the panel and wired prox and motor to terminal block and contractors (With motor overload). There is brand new PLC in the control panel and I want to know the steps I am going to follow as a PLC programmer.

1. We are using compact logix L24ER-QB1B processor and it will factory flash with firmware 1.xx version and first thing I am going to do is assigning an IP address to my PLC and connect through my PC.

2. Then I will update the firmware according to my rslogix 5k software and as I am using version 20.04 so I will be flashing my PLC processor with the same version. I get that version compatibility from AB website and link is
below
https://ibb.co/eku1dk

quick question: Should I use USB or Ethernet/IP driver to flash the firmware? Which one would you guys recommend, I never flashed any PLC before but I will be using AB manual to follow the steps but most important thing I know about flashing a firmware never breaks the communication otherwise I will brick my PLC



3. Now, I have processor flashed with version 20.04 and I have PLC program which is also v20.04, I can get online and download the program and troubleshoot a little bit to make conveyor system work how I want it.

Is there any important step I am missing here? Please tell me I would really appreciate that!

Thank you,
  Reply With Quote
Old September 25th, 2017, 06:48 AM   #2
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 391
Pretty much as you describe, there is no secret way. For an out of the box new CPU, I just use the USB, its so much easier.

Set the IP in Linx and then just go online in RS Logix and update the firmware and download.

You can do it all from the USB.
  Reply With Quote
Old September 25th, 2017, 07:23 AM   #3
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 181
Janner_10,
Awesome! thank you
  Reply With Quote
Old September 25th, 2017, 07:24 AM   #4
Helliana
Member
United States

Helliana is offline
 
Join Date: Nov 2011
Location: Arkansas
Posts: 553
You have the basic steps down. On the newer Control/Compact Logix processors with the built in USB port, there is not much difference between using USB and the network connection. On the old processors with the RS232 serial port, it would take FOREVER to flash over it. I usually use the USB serial port to connect to the processor the first time and set the IP address via RSLinx. Corporate IT group policy firewall rules on my laptop prevent BootP from working correctly most of the time, so I have given up on that and use the USB port.
  Reply With Quote
Old September 25th, 2017, 07:29 AM   #5
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 181
Quote:
Originally Posted by Helliana View Post
You have the basic steps down. On the newer Control/Compact Logix processors with the built-in USB port, there is not much difference between using USB and the network connection. On the old processors with the RS232 serial port, it would take FOREVER to flash over it. I usually use the USB serial port to connect tot he processor the first time and set the IP address via RSLinx. Corporate IT group policy firewall rules on my laptop prevent BootP from working correctly most of the time, so I have given up on that and use the USB port.
Helliana,

So I will use USB cable to connect with my PLC for the first time and then I can set the IP address of my processor for the first time and I will make sure it's static so won't change if the power goes down. Once I have my IP assigned, either I can leave it connected on USB or connect with ethernet/IP. Personally, I would like to connect with ethernet/IP driver because the wire could be pretty long and I can move my laptop a little bit if I have to. Because the A to B USB cable I have is not very long enough to move around.

Thanks for the input though!

Best,
  Reply With Quote
Old September 25th, 2017, 12:03 PM   #6
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 356
+1 for USB. I always use USB for the new hardware because it's plug in and go. Makes the whole process easier.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old September 25th, 2017, 12:04 PM   #7
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 356
Also, congrats on landing the position
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old September 25th, 2017, 12:08 PM   #8
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 181
Quote:
Originally Posted by LoganB View Post
Also, congrats on landing the position
Thank you LoganB, I havent started working as a junior Control engineer yet. The interview went pretty good but still waiting for their reply. I am doing this project at my current workplace! But thanks anyways

Quick question about USB connection, I agree with you USB is pretty easy but I was reading AB manual and they mentioned don't remove the USB cable while the processor is powered up. Is that true?

Also, I was thinking to leave the cable in the processor all the time and whenever I have to make any change or get online, just take my laptop and connect another side of the cable to the laptop and that's it.

What would you recommend?

Thanks
  Reply With Quote
Old September 25th, 2017, 12:59 PM   #9
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 356
I've personally removed the USB cable while the PLC was powered up many times and never had an issue... I think the warning you are referring to is an arc warning for hazardous areas. It says that removing any cable while the controller is under power could cause an arc which could theoretically cause an explosion if you were in an area with flammable vapors.

I don't believe there is any inherent danger to the controller itself to remove the USB cable while powered, as long as you aren't in the process of downloading/uploading or anything like that.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old September 25th, 2017, 01:01 PM   #10
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 356
As far as leaving the cable plugged into the processor while you aren't using it, as long as the cable is stored safely and not putting too much stress on the connector (from hanging with too much of the cable off the ground for example) you should be fine!
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old September 25th, 2017, 01:05 PM   #11
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 181
Awesome! Thank you LoganB!

You have a good day!
  Reply With Quote
Old September 25th, 2017, 04:33 PM   #12
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,129
USB flashing is virtually impossible...

Hi,

Just a quick "did you know" on using the USB port to flash the firmware for the newer Logix controllers...

Many users are leveraging virtualization to segregate the many software configurations that they are required to use. However, to flash a Logix controller via USB, both ControlFlash and RSLinx Classic, running the USB/VBP driver, must be running on the Host system and not in a virtual session, such as VMware. You can only flash controllers while running ControlFlash and RSLinx Classic in a virtual session with an Ethernet driver.

Once flashed, you can then use a USB driver and cable from within a virtual session to connect to the controller for download/upload and online programming, etc.

It's just a heads up for those already using USB as their go-to controller flashing method. You might find if you're ever attempting a virtualized Logix controller flash that your tried and trusted USB won't be so tried or trustworthy.

Rrgards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Old October 1st, 2017, 06:40 PM   #13
keshik
Lifetime Supporting Member
Canada

keshik is offline
 
Join Date: Jun 2011
Location: Portland, OR
Posts: 350
Quote:
Originally Posted by Geospark View Post
Hi,

Just a quick "did you know" on using the USB port to flash the firmware for the newer Logix controllers...

Many users are leveraging virtualization to segregate the many software configurations that they are required to use. However, to flash a Logix controller via USB, both ControlFlash and RSLinx Classic, running the USB/VBP driver, must be running on the Host system and not in a virtual session, such as VMware. You can only flash controllers while running ControlFlash and RSLinx Classic in a virtual session with an Ethernet driver.

Once flashed, you can then use a USB driver and cable from within a virtual session to connect to the controller for download/upload and online programming, etc.

It's just a heads up for those already using USB as their go-to controller flashing method. You might find if you're ever attempting a virtualized Logix controller flash that your tried and trusted USB won't be so tried or trustworthy.

Rrgards,
George
George, are you sure about this? I just flashed a CompactLogix PLC in a virtual machine over USB with no issues.

Windows 10 Pro, Windows 7 Pro in VMWare Workstation Pro 12.5.
RSLinx 3.90
1769-L30ER to v24.013.16
ControFLASH 12.01.00
  Reply With Quote
Old October 2nd, 2017, 01:02 AM   #14
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 391
Quote:
Originally Posted by Geospark View Post
Hi,

Just a quick "did you know" on using the USB port to flash the firmware for the newer Logix controllers...

Many users are leveraging virtualization to segregate the many software configurations that they are required to use. However, to flash a Logix controller via USB, both ControlFlash and RSLinx Classic, running the USB/VBP driver, must be running on the Host system and not in a virtual session, such as VMware. You can only flash controllers while running ControlFlash and RSLinx Classic in a virtual session with an Ethernet driver.

Once flashed, you can then use a USB driver and cable from within a virtual session to connect to the controller for download/upload and online programming, etc.

It's just a heads up for those already using USB as their go-to controller flashing method. You might find if you're ever attempting a virtualized Logix controller flash that your tried and trusted USB won't be so tried or trustworthy.

Rrgards,
George
Thats not the case, at least with us anyway. We all have AB VM's and have no problem flashing.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC For Senior Capstone Project #FFFFFF LIVE PLC Questions And Answers 6 April 20th, 2017 09:39 AM
Can RSLogix show me difference b/t project in PLC and laptop? unsaint32 LIVE PLC Questions And Answers 2 September 1st, 2014 08:51 PM
Real World Project AndrewM LIVE PLC Questions And Answers 0 November 23rd, 2011 08:35 AM
Need help to chose PLC base final year project engr.irfankhan LIVE PLC Questions And Answers 3 April 26th, 2011 05:30 PM
Networking (siemens) after preparing the project...steps drspanda LIVE PLC Questions And Answers 4 September 22nd, 2007 10:16 AM


All times are GMT -5. The time now is 09:23 PM.


.