FactoryTalk View Studio - ME/SE Alarms

We have a fair amount of different ME projects that we occasionally have to bring into a SE project. Is there a good way to bring the alarms over without having to spend a lot of time reworking them? Is there a better way to structure them in ME to make it easier?


Thanks.
  Reply With Quote
Old November 18th, 2017, 02:13 AM   #2
chavak
Member
Malaysia

chavak is offline
 
chavak's Avatar
 
Join Date: Jul 2002
Posts: 613
I like to trigger it by value rather than bits.
Reduce the hassle of mapping the amount of bit tags.
______
  Reply With Quote
Old November 20th, 2017, 01:29 PM   #3
keshik
Lifetime Supporting Member
Canada

keshik is offline
 
Join Date: Jun 2011
Location: Portland, OR
Posts: 350
Is that for ME only? Does that transfer easier to SE?
  Reply With Quote
Old November 21st, 2017, 12:27 PM   #4
arlenjacobs
Lifetime Supporting Member
Canada

arlenjacobs is offline
 
Join Date: Sep 2014
Location: Kelowna
Posts: 554
Quote:
Originally Posted by keshik View Post
We have a fair amount of different ME projects that we occasionally have to bring into a SE project. Is there a good way to bring the alarms over without having to spend a lot of time reworking them? Is there a better way to structure them in ME to make it easier?


Thanks.
No, there is no easy way to bring them into SE.
The alarm systems are so very different; SE is threshold based alarms and ME is trigger (exact value) based alarms.

To make it easiest, be sure to only use HMI digital tags for your alarm triggers.
Do not use an analog trigger, with multiple values. Do not use expressions.
Neither of those are easy to bring into SE.


The HMI alarms in SE are tag based, and all their configuration is in the HMI tag database (that excludes the other alarming system in SE; FT Alarms and Events). The one benefit of the SE alarms is that you can use the Tag Import/Export tool to export the SE HMI tag alarms to CSV. That can make edits for import a lot quicker.


These would be the steps that I would use:
1)Export the ME tags to *.csv file. Export the alarms to *.xml file.
2)Import the tags *.csv into your SE project
3)Create a couple HMI alarms in your SE project (as an example template for the csv file)
4)Export the SE alarms and tags to CSV.


At this point you can either try to use the alarms.xml file in Excel (it's not easy to learn how to use xml files in Excel).
Or, you can open the Alarm Editor in ME and just copy paste all the alarm message rows into Excel. Then manually format into the SE alarms.csv file.


That's it. That's the way to do it.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Factorytalk View Studio Machine 5.1 won't launch Martindag LIVE PLC Questions And Answers 12 February 17th, 2016 10:14 AM
FactoryTalk View Studio -Shortcut problems after Creating Runtime Application Rob S. LIVE PLC Questions And Answers 3 February 9th, 2016 11:00 PM
FactoryTalk View Studio Failed robinyin LIVE PLC Questions And Answers 2 January 14th, 2016 02:03 PM
FactoryTalk View Studio Getting data from other software fhervrylesestoso LIVE PLC Questions And Answers 2 February 3rd, 2014 03:54 AM
FactoryTalk View Studio SE Alarms & Events timestamp question jmveerkamp LIVE PLC Questions And Answers 2 August 13th, 2012 08:00 AM


All times are GMT -5. The time now is 04:15 PM.


.