Hi guys,
Some of you may remember me mentioning a backup Profibus connection I have in my project. A quick recap:
1. Existing Profibus connection between Main Control Panel at water treatment plant, and Lake Intake Pump Station (about 0.5 miles away).
2. Profibus wiring is existing, and worked just fine with old PLCs (Siemens S7). So far as I know, it hasn't been touched during the panel swap other than to land it onto surge suppressors (which I've disconnected entirely to reduce variables).
3. I'm using a MVI56-PDPMV1 at the Main Control Panel (address 0) and an ILX69-PBS at the Lake Intake Pump Station (address 10). These are the only things connected to the Profibus network (and were the only things connected previously as well, save that the old system piggy-backed through the Main Control Panel's PG port via a CP5611 for the HMI's access; that's all been removed and now the Profibus is simply a backup for the fiber link between the Main Control Panel and the Lake Intake Pump Station).
4. I have terminating resistors switched "on" at both ends. The connector at the Main Control Panel is being reused from old system, it has a PG port. The connector at the Lake Intake Pump Station is new, and doesn't have a PG port. I've wired Green to A1, and Red to A2 on both sides (no crossover or anything).
5. When I use the Prosoft Configuration Builder to set up the Profibus connection, if I scan the network only the master shows up; the slave has never showed up.
6. If I go to "monitor/modify" in Prosoft Configuration Builder, the slave has a red border around its icon. If I go to its diagnostics tab, the error is that the slave is "not existant".
7. I've re-terminated both sides of the Profibus connection; the old terminations were kind of hammered so I re-stripped the outer insulation, made sure there was a good connection to the shield, and re-stripped both A and B conductors too.
8. If I measure voltage across the A and B conductors in the connector, I get about 0.5-0.6VDC. But according to my ohm's law calcs across the differential, the voltage should be about 1.0VDC (the supply voltage is 5.0VDC).
9. If I go to the diagnostics webpage for the ILX69-PBS it says under the Module Status:
They seem to believe it is a physical connection problem since the configured slave should show up on a scan, and since it isn't there's not much else to try. We did have surge protectors in line with the connections, but to make everything as simple as possible I have entirely bypassed them and have wired everything directly (to no avail).
If anyone has anything to suggest looking into, it would be amazingly helpful. Thanks a bunch.
Some of you may remember me mentioning a backup Profibus connection I have in my project. A quick recap:
1. Existing Profibus connection between Main Control Panel at water treatment plant, and Lake Intake Pump Station (about 0.5 miles away).
2. Profibus wiring is existing, and worked just fine with old PLCs (Siemens S7). So far as I know, it hasn't been touched during the panel swap other than to land it onto surge suppressors (which I've disconnected entirely to reduce variables).
3. I'm using a MVI56-PDPMV1 at the Main Control Panel (address 0) and an ILX69-PBS at the Lake Intake Pump Station (address 10). These are the only things connected to the Profibus network (and were the only things connected previously as well, save that the old system piggy-backed through the Main Control Panel's PG port via a CP5611 for the HMI's access; that's all been removed and now the Profibus is simply a backup for the fiber link between the Main Control Panel and the Lake Intake Pump Station).
4. I have terminating resistors switched "on" at both ends. The connector at the Main Control Panel is being reused from old system, it has a PG port. The connector at the Lake Intake Pump Station is new, and doesn't have a PG port. I've wired Green to A1, and Red to A2 on both sides (no crossover or anything).
5. When I use the Prosoft Configuration Builder to set up the Profibus connection, if I scan the network only the master shows up; the slave has never showed up.
6. If I go to "monitor/modify" in Prosoft Configuration Builder, the slave has a red border around its icon. If I go to its diagnostics tab, the error is that the slave is "not existant".
7. I've re-terminated both sides of the Profibus connection; the old terminations were kind of hammered so I re-stripped the outer insulation, made sure there was a good connection to the shield, and re-stripped both A and B conductors too.
8. If I measure voltage across the A and B conductors in the connector, I get about 0.5-0.6VDC. But according to my ohm's law calcs across the differential, the voltage should be about 1.0VDC (the supply voltage is 5.0VDC).
9. If I go to the diagnostics webpage for the ILX69-PBS it says under the Module Status:
Status: Configured
Uptime: 12 days, 05:23:52
Network State: Stop
Communicating: No
Running: Yes
Ready: Yes
Error: No
Bus ON: Yes
Config Lock: No
Communication Error: 0x00000000
Error Counter: 0
Watchdog Time: 20
And under the Network Status:Uptime: 12 days, 05:23:52
Network State: Stop
Communicating: No
Running: Yes
Ready: Yes
Error: No
Bus ON: Yes
Config Lock: No
Communication Error: 0x00000000
Error Counter: 0
Watchdog Time: 20
Baud Rate: Not Detected
Bus Address: 10
Ident Number: 0x0EE1
Receive Data Length: 0
Bytes Transmit Data Length: 0
Bytes Error Count: 0
Last Error: 0
Network Activity: 0
At this point I have no idea what else to do. I have a call in to Prosoft but they're not going to be able to get back to me until tomorrow as the engineer assigned to my call has left for the day. Bus Address: 10
Ident Number: 0x0EE1
Receive Data Length: 0
Bytes Transmit Data Length: 0
Bytes Error Count: 0
Last Error: 0
Network Activity: 0
They seem to believe it is a physical connection problem since the configured slave should show up on a scan, and since it isn't there's not much else to try. We did have surge protectors in line with the connections, but to make everything as simple as possible I have entirely bypassed them and have wired everything directly (to no avail).
If anyone has anything to suggest looking into, it would be amazingly helpful. Thanks a bunch.