I am almost 100% sure this is related to the issue with the customer losing the 5069-IF8 input module the other day, but alas, it's another strange one I've never seen. I get a call about several control valves on I/Ps that are "hissing" every 10-15 seconds. Also the LEDs on the channels on the card itself would flash red every time this happened. I looked and the valve output is completely closed (20mA - reverse acting), and steady. I had them put a meter on one of the spare channels that I set to 20mA and told them to watch it next time the LEDs flash red. Sure enough, the output dropped to 0mA and came right back up to 20mA. No faults on the card, and as far as the PLC can tell, it's healthy. 24vdc power supply is rock steady with no dips.
My money is on another card failure.
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
107
Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the...
399
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
542
Hi all, have a project which requires reading a weigh head weight over ASCII. Never really touched ascii so struggling a bit. The weigh head is in...
1,241
Hello, I have a laying out a system that will have a CompactLogix rack and I had a question on the power for the inputs and outputs. I was...
373