Panelview 800 Can't connect to Laptop. rslinx can't find.

Why does this problem happen?

Thank you for post, it solve my problem.

Why does this problem happen?

I have recreated the same problem using IP explorer while enabling BooTP mode. Sometimes it goes well, but sometimes there is an error message which causes the problem where we have to reset the HMI. Replacing the firmware does not solve the problem!

IMG_0283.jpg
 
Problem solved

I finally did a factory reset.

1-Connect an external USB keyboard to the terminal
2-Hold the Ctrl and Shift keys simultaneously
3-A dialog box appears with the prompt: Return to Out of Box Condition?
4-Press the Yes or F1 to return to the out-of-box condition, or press the No or F2 to
cancel.

And the problem was solved.

This worked for me, but just appeared on RSLinx when I used the IP range "192.168.1.XXX".
 

Similar Topics

Hi there, I'm wanting to connect a panelview 800 to an SLC5/03 the SLC is connected to an 1747-AIC which is run to another 1747-AIC. I'm trying...
Replies
0
Views
1,553
As the title says, I'm using CCW with a PV800 (and Micro850). I've made a scheduler in which a user can choose a month, day (1-31), hour (0-23)...
Replies
15
Views
502
Hello, So i managed to read the string coming from control logix and put a string display in PanelView 800. Now I am struggling to do the other...
Replies
1
Views
136
Good morning all, programming a Panelview 800, I have a maintained push button programmed on screen 1. I copied and pasted it to screen 2. Could...
Replies
2
Views
1,152
I'm trying to convert an old panelview 600 application to the 800 and I'd like to keep the current serial comms configuration instead of adding...
Replies
1
Views
588
Back
Top Bottom