I_Automation
Lifetime Supporting Member
I took his 'Modules" as the DeviceNet socket part, not the Input and Output modules plugged in them.
Exactly, those connections form the 'backplane' such as it is (and the literature does indeed call it a backplane, which is why I do as well).When plvlce says back pane he means the down stream modules of the adapter as you noted these are tongue and groove connections.
I attempted to consistently use 'module' for what you are now calling 'card' to be consistent with the nomenclature you were using at the time (eg "Node 20 has the Network LED's flashing constantly on 3 modules)I took his 'Modules" as the DeviceNet socket part, not the Input and Output modules plugged in them.
I had not remembered Point I/O being that finicky about revision, but one of the real disadvantages of DeviceNet imo is needing RSNetworx for even minor changes like that.
Surprised to hear that a separate power supply for outputs would cause an issue -- the FPD should be completely transparent to the adapter.
Glad to hear you were getting things sorted out though.
How did you go after you wake up phone call?
No idea why you'd have a difference in behaviour between the two nodes.Could not remove module 10 on node 20 and download the new configuration - it still reports the processor was in Run mode and would not download. So I had to leave the unused output module installed. Even going in the PLC and shutting off the DeviceNet adapter so I could download to it did not take Node 20 out of Run. Downloading to Node 10 was allowed even though it was running. Nothing on Rockwell.com about this other than "take it out of run." No mode switch on the ADN or anything to click in RSNetworx I found.
In the subnet, open the Properties for the individual output card and under the Configuration tab look for a series of parameters labeled "Enable No Load" (one parameter for each output). Set them to disabled.It finally came up running but after a few seconds Node 20 showed red even though it was working. Digging down found output 10 giving 8 errors of nothing connected to the output.
At least this got the faults clear and the press running, but this system is not being used this job. I told the customer that if the "Nothing Attached" is a problem when they put the next job in to add 8 pilot lights to the 8 outputs, just they would never light.
I couldn't see how you would tell it that an individual output wasn't in use, but can't imaging whoever designed this figured that every output on every module was going to be used with none extra & empty.
Indeed, 'Full' does not include RSNetworx...The only thing is I had to find an older version of Studio 5000 that included RSNetworx, as the newest v32 and all v33 don't include it anymore. Then, even though I have Studio Full Edition, that is supposed to include everything, it doesn't license RSNetworx and had to run on a grace period license.
Obviously some one did not listen!