Hi Everyone,
Looking for a "Sanity Check" on my programming for Starting and Stopping a pump connected to a SMC-3 Flex Soft Starter via Ethernet/IP. I have never used EIP with a Flex before so I want to make sure I am on the right track.

I am basically using the same logic that I use with a Powerflex VFD. I set the Start Bit until the Running Bit is true. Then I set the Stop Bit until the Stopping Bit is true. I have 2 diffrent devices that can request the pump to run so I have the Start Request's OR'd together and the Stop Request AND'd together.

Give me your thoughts on this.
Thanks!!

SMC Pump Start_Stop.jpg
 
SMC-3 is one version of a Rockwell soft starter, SMC-Flex is a different version. There is no SMC-3 Flex...

Given that the SMC-3 is not digital and cannot therefore have an Ethernet interface, I suspect you have an SMC-Flex. If that's the case, I see nothing wrong with your logic, but I can't really read it all that well.
 
Yes it is a SMC-Flex. I must have looked at the Spec Sheet from the vendor wrong to get the SMC-3. The 3 is the position of the soft starter.

How can I get the Snip to post with a better resolution? It is hard to read this way.
 
...

How can I get the Snip to post with a better resolution? It is hard to read this way.
Narrow your ladder view just to the point before it rung-wraps. Screen shot just the ladder window. Use paint.net (www.getpaint.net) if necessary to crop, resize save with compression to met forum requirements. Mainly the first thing though, narrow your ladder view window as much as possible.
 

Similar Topics

An outside contracting firm designed a machine for our company. There are several devices connected through Ethernet/IP. This includes a Panel...
Replies
4
Views
180
Hey everyone! I'm searching for an example demonstrating how to program in Studio 5000 speed control of a PowerFlex 525 drive via Ethernet. While...
Replies
1
Views
639
I have a system that is using TCP sockets. There are 5 connections between the Ethernet card and the end devices (smart conveying system)...
Replies
0
Views
691
I am trying to exchange data (N registers) to and from a Control Logix PLC. I am programming the messages in the Control Logix program, to...
Replies
7
Views
2,125
Hi I’m having issues figuring out how to connect a Schneider ATV930 to Control Logix PLC. Can’t figure out the Connection Parameters, I used the...
Replies
2
Views
1,168
Back
Top Bottom