Hi all,
I'm working on a project monitoring DLR rings using explicit messaging - (Citect SCADA ABCLX driver + 1765-L62 v20.19)
Just a few questions, (first time working with DLR and don't really have enough hardware to test currently).
1.
The PLC is the supervisor, Precedence = 0, all the devices on the ring are ETAPs with 2-10 pumps in star topology.
Is there ever a situation that I would have to consider (for monitoring) when the PLC is not the Supervisor?
If i lose the PLC (Citect IO Device), the next tap will become supervisor, but no point in programming for this case as we wont be able to see anything?
2.
Get Ring Participant list:
CIP Generic: Get Attribute Single
Service Code: e
Class=0x47
Instance=1
Attribute=9
This is returning an array of SINT's (10 SINT for each node found). I was wondering is there any defined order for the list? aka, it is in order found along the network out of port 1 and into port 2 ?
I wanto compare the returned MAC address's in this list to generate "Link Faulted" Graphics.
Any documents that actually give detailed information on the DLR CIP commands would be awesome, so far the following only have examples and don't really tell the whole story:
290e-at001_-en-p.pdf - ArmorStart® DLR Reference Architecture
enet-at007_-en-p.pdf - Application Technique Ethernet IP Device Level Ring
It isn't even mentioned in the EthernetNet I/P CIP Standard: Vol2_1.28 !?!:eek:
Cheers!:p
The participant list goes from the lower numbered port on the active supervisor, where Suervisor takes first record.
Please note that Get Single message is limited to 49 nodes, because of 492 bytes CIP payload limit. The alternative is to use Get Member service, however Logic does not support that service.
My recommendation is to use DLR Faceplate AOI that already does what you are trying to do.
You can build you own HMI graphics using the same AOI.
DLR faceplate is available under PCDC Network Device Library.
hi,
I tried to find sample code in Rockwell library. but not found
can you share link for same where i can download "DLR_AOI" or "AB_DLR." faceplate
I'm looking online in a Project trying to catch a Jam instant. I'm looking at the Logic of this AOI where I found the only instant of a Jam Photo...
5,318
With the help of this forum, I had a plc replacement project signed off today, this is not my day job and haven't done plc stuff for about ten...
69
19,502
Hello, I am looking for a product to help me better understand logic control systems. I have been working with Allen Bradley PLCs for about 3...
2,472
Hello, I have a question on furthering my education and what you guys think would prepare me for the future in automation. I have a 2yr diploma in...
4,647
Anyone know what these statistics mean or if there is a page that explains it more? I couldn't find anything on Rockwell's website or literature...
57