What do you mean by barrier?? And where are you planning on installing these?

The output seems mapped from 4-20mA, so it can go directly into the PLC input if configured correctly.
 
By barrier, I suppose you mean a signal isolator? If you look at the specs on that NK unit, it says that the isolation voltage is UL listed at 1270V, tested to 3000V. That's better than most of the little "terminal block" style signal isolators you find (Phoenix Contact is 375V for example). You are good to go.

+1 on NK Technologies by the way. They are my go-to guys.
 
Thanks for answers!

What do you mean by barrier?? And where are you planning on installing these?

The output seems mapped from 4-20mA, so it can go directly into the PLC input if configured correctly.

By barrier, I suppose you mean a signal isolator? If you look at the specs on that NK unit, it says that the isolation voltage is UL listed at 1270V, tested to 3000V. That's better than most of the little "terminal block" style signal isolators you find (Phoenix Contact is 375V for example). You are good to go.

+1 on NK Technologies by the way. They are my go-to guys.

Yes this is what I meant to say. Signal isolator.

This should measure Amps that DC motor takes during connection (tightening) of drill pipes on drilling rig. Then from that measurement PLC should calculate Torque applied on drill pipe.
 

Similar Topics

Today I was working on my project for school and we were using a power supply with 24V and we accidentally had the current at 0.9A. We heard a pop...
Replies
9
Views
497
Hi all, I have been working on a project that requires me to measure the current across a 90 VDC motor of a medical device (similar to an...
Replies
25
Views
1,295
HI i have a delta VFD M-series in the manual, in order to enter the motor rated current you set the parameter P,52 =the motor rated current my...
Replies
7
Views
634
HI! HOW COULD I OBTAIN THE NAMES OF THE STEPS OF A ROUTINE IN SFC LANGUAGE IN STUDIO5000? Or is there a system variable that gives me those...
Replies
0
Views
331
VFD is not tripping at higher current , resulting in motor failure . VFD Model : Make - KEB Type - H6- 10H6BBBB-21B0
Replies
2
Views
501
Back
Top Bottom