I have a old PanelView standard 600 I plan on using in my garage for setting up security.
The garage is about 60 feet from the house SLC-500 and 5/04. I have a 2711-NC22 cable that needs be about another 20 feet longer at least..
What would be a good solution to get it to work? Can I get a longer serial cable? Or what do I need to get it to communicate on Ethernet?
Thank you
The 2711-K6C5L1 terminal has an RS-232 port that runs DH485 protocol.
You could connect it to an SLC-5/04 with a straight-through RS-232 serial cable, for which the typical maximum length is 50 feet.
I've run low-capacitance cable with RS-232 signals for about 200 feet with good success. 60 or 70 feet isn't stretching the 50-foot limit of RS-232 by very much.
There is no practical way to connect this terminal to Ethernet. There are a couple of *impractical* ways, with network gateways, but those are far too expensive for a home rig.
Your PV supports DH485 protocol.
Your 2711-NC22 cable will not work, the round port on your SLC5/04 is DH+ protocol and cannot be changed to DH485.
You will have to use the 9 pin serial port on the SLC5/04 configured for DH485 protocol.
60 feet should not be a problem. A 2711-NC14 is the proper cable ( its just a straight thru cable, make your own)
Edit: Ken types faster.
Is the communication cable for this PanelView a straight through 9 pin cable? It uses DH-485. The manual doesn't say if it is or not. Thanks a...
1,861
Hello, Friends Please someone help me find right cable to communicate Panelview 600 (2711-B6C9) to Micrologix 1200 (1762-L24AWAR). AND any advice.
269
Client has multiple spare Panelview 550 (2711-T5A10 L1 PV550 Touch Devicenet)...
686
I'm a beginner to PLC and Hmi programming. any one please help how to connect HMI to pc. HMI has a printer **** enabled by default, It does not...
424
need instruction on how to download an existing program to the PV. I am very new to PLC's they came with the job so now sink or swim don't want to...
907