Kinetix 5500 Active homing - using PLC tag instead of hardwired inputs?

Hello PLCs.net!

I have a kinetix 5500 drive connected to a gantry, I was wondering if there is a way to do active homing using a PLC tag?
At this moment, the AOP asked me to just go into the digital inputs tab and reassign one of the inputs as a homing input, currently the digital inputs 1&2 are used for positive and negative overtravel, so no spares.

Has anyone done homing through a PLC tag?
Regards,
-PreLC
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.
  Reply With Quote
Old January 14th, 2021, 01:36 PM   #2
dmroeder
Lifetime Supporting Member
United States

dmroeder is offline
 
dmroeder's Avatar
 
Join Date: Apr 2006
Location: Vancouver, WA
Posts: 2,717
It is possible. There is a technote, I'll find it in a bit. It involves sending a message to change one of the over travels to a home input. So basically, when you know you need to home, you MSG to change the negative over travel (for example) to a home input, issue a MAH, when complete, you MSG to change the input back to an overtravel.

KB: QA28637, techconnect level

Last edited by dmroeder; January 14th, 2021 at 01:44 PM.
  Reply With Quote
Old January 14th, 2021, 06:33 PM   #3
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 331
Quote:
Originally Posted by dmroeder View Post
It is possible. There is a technote, I'll find it in a bit. It involves sending a message to change one of the over travels to a home input. So basically, when you know you need to home, you MSG to change the negative over travel (for example) to a home input, issue a MAH, when complete, you MSG to change the input back to an overtravel.

KB: QA28637, techconnect level
Hmm. I guess we just need it wired to the drive itself.

Crazy question, for homing, have you used prox switches rather than actial limit switches?
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.
  Reply With Quote
Old January 14th, 2021, 06:42 PM   #4
dmroeder
Lifetime Supporting Member
United States

dmroeder is offline
 
dmroeder's Avatar
 
Join Date: Apr 2006
Location: Vancouver, WA
Posts: 2,717
Quote:
Originally Posted by PreLC View Post
Crazy question, for homing, have you used prox switches rather than actial limit switches?
Sure, I can't think of a time where we have ever used limit switches. We will generally use a prox or a photocell, depending on the application.
  Reply With Quote
Old January 14th, 2021, 06:52 PM   #5
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 331
Quote:
Originally Posted by dmroeder View Post
Sure, I can't think of a time where we have ever used limit switches. We will generally use a prox or a photocell, depending on the application.
Thanks for the help DM, always appreciate it.
Huh. We just ordered a precision limit switch in order to home a table for a position-critical drilling machine. Haven't installed it yet, but it does have existing overtravel sensors. Do you think we should try active homing with those first? Also, what type of active homing would you recommend?
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.
  Reply With Quote
Old January 14th, 2021, 07:22 PM   #6
dmroeder
Lifetime Supporting Member
United States

dmroeder is offline
 
dmroeder's Avatar
 
Join Date: Apr 2006
Location: Vancouver, WA
Posts: 2,717
Quote:
Originally Posted by PreLC View Post
Thanks for the help DM, always appreciate it.
Huh. We just ordered a precision limit switch in order to home a table for a position-critical drilling machine. Haven't installed it yet, but it does have existing overtravel sensors. Do you think we should try active homing with those first? Also, what type of active homing would you recommend?
I'll defer to someone smarter than me, the stuff we are doing isn't super precise. Speed, power is generally what we are after, precision is a bonus.
  Reply With Quote
Old January 14th, 2021, 08:36 PM   #7
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is online now
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 7,459
For homing to a switch I like:
1. Move to actuate the home switch.
2. Reverse direction at very low speed until clear of the home switch.
3. Stop at the next encoder marker pulse and set the current axis position to be the home position including any offset.

The existence of step 3 allows for some variation in the actuation positions of the home switch each time you perform a homing routine. The final stopping position will be consistent.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Schneider Unity Pro - PLC vs Local Init Values & Current Tag Values 123MB LIVE PLC Questions And Answers 5 October 22nd, 2019 12:35 AM
Changing Homing -> Position programmatically, Kinetix 5500. Elcan LIVE PLC Questions And Answers 3 November 27th, 2018 07:37 AM
PV 1000 Error 362 LMBrian LIVE PLC Questions And Answers 5 November 21st, 2018 04:14 PM
MPI comunication Manuel Raposo LIVE PLC Questions And Answers 22 July 16th, 2007 07:24 AM
RCDs on PLC inputs Doug_Adam LIVE PLC Questions And Answers 8 February 23rd, 2003 11:17 PM


All times are GMT -4. The time now is 05:59 PM.


.