Why rated current of an inverter decrease when working temperature increase?

Most electrical equipment is rated (ampacity or Kw) on the ability to keep it cool or more accurately its ability to shed waste heat. That is why if you look at conductor ratings in Natl Electric Code you will see a large difference between those in conduit and those in free air. Higher A M B I E N T temperatures reduce ability to shed waste heat therefore you must derate it to avoid burnout.

The reason higher altitude causes derate is the air is less dense and has less ability to transfer the heat from equipment.

Dan Bentler
 
Think of it this way, if you take a wire with insulation and start to heat it up what happens to the insulation? It melts off. The same type of thing holds true with electronics, the silicone, germanium and other materials used in making the internal items of the electronic components starts to break down as it gets hotter as well. So if you dont have the heat dissapation then your component is going to fail prematurely, hence derate for safety and longevity.
 

Similar Topics

HI i have a delta VFD M-series in the manual, in order to enter the motor rated current you set the parameter P,52 =the motor rated current my...
Replies
7
Views
652
Off topic, but you people here usually have pretty good suggestions. Title kind of says it, anyone know of a DC current switch that has a decent...
Replies
1
Views
731
My turn to post a non-plc related question. Believe it or not, it's drive related. Most drive manufacturers specify the overload capacity of...
Replies
4
Views
7,089
How do I get the mV or weight readings for individual load cells connected to summing board into the PLC? Do I use a MSG instruction and what are...
Replies
3
Views
644
Hi all, I have an IDC from Rockwell, and it is super old, but new (had it in the spares). The previous one has gone faulty, and I need to set...
Replies
6
Views
1,451
Back
Top Bottom