Using the "bias" parameter on a AB 1771-IR RTD card
zonk
Sep 2005
Iowa
A customer of mine is having problems with the accuracy of an RTD that is wired into an AB 1771-IR RTD card. The RTD is off by 5.2 degrees F at 32 degrees (37.2). I replaced the RTD with a new one and had the same result. I moved the wires to a new point on the card and got the same reading.
After doing some research, I found that if the resistance on the lead wires on a three wire RTD are not matched, it can cause an accurracy error. I believe this is the case.
My question is this: Instead of replacing the wiring, my customer would like to use the bias parameter on the RTD card configuration to correct the reading. Is that what the bias parameter on the 1771-IR is used for?
I cannot find any documentation that describes the function of the parameter in any detail.
Also, if you know of a good paper on the proper installation and wiring of RTDs that would be a big help.
The bias setting (in BCD) is subtracted from the Channel data. So, if you want to give a shot, enter 5.2 into the bias and recheck at 32, the input value should be 37.2-5.2=32, you should also check at some other value to see if the offset is the same through out the range of the RTD.
If you know the guage and length of the wire you can calculate the temperature shift it causes. Just figure the resistance out and back, and go to a RTD resistance vs. temperature table, add it to the resistance for the expected temperature, and look up the new temperature. If worst comes to worst you can deduct the increase in your logic rather than configure the card.
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
54
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
115
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
221
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
59
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
104