How to configure Panel view plus 6 auto start in Factory Talk ME

IdealDan

Member
Join Date
May 2017
Location
MA
Posts
480
Hi Friends,
Pls, where in Factory Talk View studio ME is the option for configuring Panel view plus 6 such that .mer can automatically run when Terminal is powered on?
Responses will be appreciated.
Regards
 
On startup look for a white square in the corner press and hold it you should get to the configuration mode
From the PanelView Plus Configuration screen, you must first Load the program you wish to start automatically. Then go to the Start Up options. "Run Application at Startup" should already be selected but you must press OK at this screen. Reset the terminal.
 
On startup look for a white square in the corner press and hold it you should get to the configuration mode
From the PanelView Plus Configuration screen, you must first Load the program you wish to start automatically. Then go to the Start Up options. "Run Application at Startup" should already be selected but you must press OK at this screen. Reset the terminal.
Thanks Bro,
I want to understand, Can it be achieved via Factory Talk? Any Option for that in Factory Talk ME?
 
im not aware of it being an option within FTVS ME, but if you connect to the PVP with the Transfer Utility and load an .mer that way there is an option box that you can check off right below the Destination Storage Type drop down menu that will tell the .mer to run at startup.
 

Similar Topics

Simple question, quick google didn't help. Is there a configuration for comfort panels to show when there is no contact to the PLC? Alternatively...
Replies
2
Views
1,902
Hello Siemens experts please help me to Configure PP17 panel on Ethernet network in S7-300 CPU315 2PN/DP. I have "S7-300 CPU315 2PN/DP" and...
Replies
0
Views
2,109
Hi All, I currently have a WinCC Flex project running on Simatic panel PC 677B with a CPU 315 2-DP PLC communicating over MPI. I would like to...
Replies
3
Views
4,645
If you shall ever have to make a WinCC Flexible panel in order to connect it to an S5 PLC via the PG port (for example for replacing an old defect...
Replies
4
Views
2,184
hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
Replies
3
Views
94
Back
Top Bottom